Results 1 to 13 of 23
    Apr 2008
    Liebert cond tube repair
    I am hoping for some advice and opinion on options for a leak repair. This one is at the tube sheet of the return loop end (not the inlet/outlet header end) of a 4-fan air cooled unit.
    Liebert offers a repair kit that consists of a 14' roll of tube that inserts into the full length of a damaged tube, and an assortment of replacement 180's and such. The instructions show cutting into and re-stubbing both ends regardless of which single end-leak it addresses.
    Now as there is only this one trouble spot, and it happens to be a fairly accessible bottom row I was considering this option; I believe I can cut out the tube sheet around the tube and enough fins to allow brazing access, then insert just several inches of the repair tube and braze that to the exiting tube end and to the new 180' loop.
    The worry is it's not a repair I've done very often through my years.
    I can see upsides being;
    -Not cutting into the end that is not leaking and which has more vibration (although light vibration as this is a remote condenser), inserting the inner tube the full length (yikes!), potentially a less expensive repair.
    Down sides;
    I have seen tube repairs with new cracks that follow up into the coil past the brazed repair spot. But I would associate that with compressor or more vigorous gas pulsation, and this plan has the reinforcing inside tube (clean and de-burred) well in to where the fins would remain.
    Any best educated guesses out there?
    Thanks ahead- And Merry Christmas out there!
    Wayne
    Portland Oregon
    I just repaired a leak in the same spot last week, I just cut the tube sheet end but taking a drill bit and drilling holes all the way around and took a pair of snips and snipped the little metal between the holes, a friend of mine used a dremal tool to do the same job. Just becareful because I have hit the tube with the drill bit end and it made another hole. Then I took and cut out the fins to get them out of the way. After all that I just laid some 15% down all the way around. Hope this helps
    do things right the first time is cheaper.
    Apr 2008
    Quote Originally Posted by ispip View Post
    ... After all that I just laid some 15% down all the way around. Hope this helps
    Just over the hole then? I've done that (damned-easy-to-melt-tube too!)
    Yeah, I'm still kinda liking the in-tube idea but which is new to me though.
    Damm, up to late again.
    Charm City--the city that bleeds
    I like your idea better than the repair kit. Having repaired more than a few Liebert discharge line elbows at the compressor, also fittings at the receiver and such, and having repaired more CHOO_CHOO discharge leaks at the tube sheet, ...well, as Rocky would say, "Go for it."
    Having said that, you could call tech support maybe and see if they have any syllables to mumble on the virtues of the repair kit, and then factor that into the equation.
    It's great to be alive and pumping oxygen!
    May 2009
    Bardstown, KY
    I have used dremel with flex shaft to get some tube sheets out of the way before. Use some 40% silver and it won't crack on you after.
    Western Wa
    I made a similar repair on a Carrier mini boxcar last summer. No kit available.
    I used a Dremel tool to cut out enough of the end sheet to get brazing access.
    Some long pointy scissors to remove enough fins to work.
    Butt-ugly, but it worked and survived record heat.
    God Bless the USA
    Portland Oregon
    Just keep in mind if you use that tube repair kit you are lowering the efficiency of heat transfer for that whole tube plus your making 4 braze joints. This kit was intended for use when you have leaks in the middle of the condenser and you don't want to cut out all those fins to get to it. If you use a low flame you will not burn threw or use that 55% flux coated rod. I have not had any trouble with 15% cracking but i have heard it can. Any way good luck to you.
    Portland Oregon
    [QUOTE=The Doctor;5333752]I like your idea better than the repair kit. Having repaired more than a few Liebert discharge line elbows at the compressor, also fittings at the receiver and such, and having repaired more CHOO_CHOO discharge leaks at the tube sheet, ...well, as Rocky would say, "Go for it."
    On the Lieberts it is REAL important that you tighten the bolts down on the compressor so they are snug to the compressor but the washer can still spin. If you have to much play it will let the compressor rock to much on pumpdown and start up. Also on older units check your discharge tube clamps because they wear threw that orange rubber insulater.
    Nov 2009
    chicago
    lieberts leaks at tube sheets are common, i use a oxy acet torch, melt metal away from leak then repair leak be gentle also i use silver solder it flows better than silfoss. thats the way i do it good luck.
    Apr 2008
    Thanks a bunch guys for the back-up. I've decided to go ahead with silver solder on the leak, and I'll have the tube kit there as plan-B. They have about thirty of these units and if I don't need the kit it'll be fine to have at the site. The thing's only about $40.
    Cheers
    Keep it safe
    Wayne
    May 2008
    Jax Fl.
    Quote Originally Posted by dilky View Post
    Same here. We then paint the steel and copper at the repair with cold galvanize spray to stop corrosion.
    Apr 2008
    .. i use a oxy acet torch, melt metal away from leak then repair leak be gentle also i use silver solder it flows better than silfoss. thats the way i do it good luck.
    Do you mean melt the steel sheet away?
    Jun 2008
    Apopka, Florida
    Quote Originally Posted by mixsit View Post
    I think he means melt away from the sheet metal, regardless you will be fine as the others stated use a drill bit / dremel and go around the tube to an then cut away the metal so you can access your leak if needed.
    I had a condenser fan motor break and had to repair the first and second row of tubes, due to damage from the motor falling into the coil while operating, destroyed the blade and had ruptured the circuit that was in operation. I had to remove very carefully about a 4" x 8" area of the fins to do the repairs, no problems just take you time and if you have a very small tip for your torch that will work the best, it did for me.
    Hope this helps,