    Just had a newer R-410A Heat Pump repaired during winter weather conditions and the tech had to evacuate the lineset. He deep vacuumed down to the 500 micron level then re-charged the system.
    Since it was too cold outside, he was unable to verify charge using Subcooling Method. Unsure of the exact lineset length, he added refrigerant and then followed the Heat Pump Charging chart to check the lineset pressures vs. indoor & outdoor temps.
    Without weighing the charge, I guess this got him pretty close and within the tolerances of the relationship chart. Since this system uses a TXV @ indoor coil, I thought the subcooling method (with superheat verification) is the most accurate way to check charge. I just want to make sure the charge is exactly right.. I know a few ounces in either direction can make a significant difference on these new high-efficiency units. I've noticed some horizontal frost bands on the outside coil at 35-40 degrees OAT that didn't happen before.
    Should I call them back in the spring-late summer and request a proper subcooling check be performed or did he get it right using the heating mode chart??
    THANKS!!
    Indoor TXV is bypassed in heating mode.
    We go back in the spring to recheck things. It is more accurate to check in cooling mode on a warm day.
    Nov 2009
    north georgia
    Did he weight the charge specified on the rating plate and then add more, or did he just add refrigerant till the pressure was good according to the chart?
    Northeast Ohio
    Quote Originally Posted by Gaskeeter View Post
    OP wrote........
    Quote Originally Posted by RockRiver View Post
    DEM
    Oct 2008
    Did not weigh the charge because lineset length was unknown. Didn't see him use a scale or anything. Whole system was not evacuated, just the lineset.
    He throttled in liquid through the suction side a few times and then said the pressure/temps matched according to the manufacturer's heating chart.
    I have been noticing the coils frosting more quickly and the whole outdoor unit froze over in about 45 mins when the OAT was only about 33-35*. Coil was entirely frozen so no airflow -- the outdoor unit fan would try to spin, but couldn't. Defrost melts it off, but defrosts are talking longer... Full 10min cycles and still not reaching termination temp of 65 (after the 10 min max time, it gets to upper 50's, but won't terminate sooner like it should if it can reach 65). I guess I could change the jumper to 30 min defrosts from 60 min, but that just seems too frequent and not efficient.
    Any ideas?
    Nov 2009
    north georgia
    Don't change the jumper,sound's like the pressure is still off a bit. You might give them a call and tell them how your system is doing.
    Jan 2010
    North Huntingdon,Pa
    on a non adjustable txv- it should be charged to mfg's subcooling specs in cooling mode-the superheat is what it is at designed subcooling
    In a cooler climate with timer defrost, I'd shoot for no more than 60 minutes. Many around here are left on 90 minutes, like the one down the street. That poor sucker spends a lot of the winter heavily frosted.
    Dec 2009
    what is your delta T between supply and return? sounds like you need to get your service tech back out.
    Aug 2011
    what is acceptble delta t temp in heatrpump heatmode?is 20 f or more is good?and what is liquid line(bigger line) temp should be in heatmode?i read some post is 110 plus ambient temp?is that right?linetemp too low remove charge,to high add charge?
    Jan 2010
    North Huntingdon,Pa
    +110 ,that was goodman's old way of charging, they now want it weighed
    PA#9377
    Your Satisfaction...Our Goal.