    Natural Draft HWH Boiler...situation....

    I was asked a personal question by a person at a facility where we were doing some repairs to the RTU's. he wanted to know if it was good or bad for a chimney to sweat water (moisture). I mentioned that is not good and what is the situation. Well, in June of 09 the area had major rains and flooding. And in the mishap his basement was flooded, so the Insurance company paid to have the antiqued boiler replace. Thus the problem started. A 105,000 BTU boiler with a 36,000 HT into a masonry chimney (1 side to the ambient) and about 12 ft expose above the roof line. Went and looked at it. TODAY was a 25 degree day and snowing like crazy. The chimney was sweating severely at the top and 3 large wet spots on the side of the house. The boiler has a motorized vent damper and 5" single wall flue pipe in the the same chase with the HWT with the HWT with a 3" single wall flue pipe. Both are going in separate holes in the same chase.
    Now before I give my experienced comment I want to see if any of the others have any input before.
    Thanks
    JB
    PS...this is located in SW PA

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    With the damper not allowing house air to keep the chimney warm during the off cycle, the cold tile is causing the condensation.

    OR

    Could be a blockage at the top too. Had that happen a couple times.

  3. #3
    Join Date
    Dec 2003
    Posts
    2,851
    Post Likes
    The chimney is so cold that it is lowering the temp of the flue gas to the dew point and its condensing. The old boiler was less efficient and had hotter flue temps. This is something that needs to be corrected. Over time it will destroy the chimney.

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Too big of a chimney. They should have lined it with the correct size liner for that total BTU.

  5. #5
    Join Date
    Aug 2006
    Location
    Pittsburgh, PA
    Posts
    14
    Post Likes
    Thread Starter
    Correct!!
    From experience I found this out years ago. So, that is what I told the gentleman that requested me to look at it. The company that installed the boiler insists that it is installed properly and stands by it.
    What I did do for him in the mean time is set the vent damper to stay open all the time to assist more heated air into the chimney. I KNOW AND REALIZE that a liner is necessary here. But I told the gentleman to insist on the installer to install one and at the price that would have been priced at the time of the installation

  6. #6
    Join Date
    Mar 2004
    Location
    CHICAGO SUBURBS
    Posts
    466
    Post Likes
    A lot of municipallities here require a liner every time you replace equipment vented into a masonary chimney.
    Some people swear by me and some at me

  7. #7
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,302
    Post Likes
    Not an option here, gots to be the right size "if" that means liner, then that whats the inspector wants to see,,,, residential or commercial.

  8. #8
    Join Date
    Aug 2006
    Location
    Pittsburgh, PA
    Posts
    14
    Post Likes
    Thread Starter
    UPDATE....I just got an email from the customer (not mine) that the company owner called and emailed them. (don't have the guts to go in person) And told them that he drove by and took pictures. And he feels that it is the flashing and the area around the chimney is leaking. So, the customer had a reputable chimney/masonry company come and look at it. They said it need a direct vent kit on the boiler and that a liner will rot away in 3 - 5 years.
    I emailed back that the chimney company should have suggested a stainless liner or at least an aluminum liner. And the direct vent is fine and they work great, but he still would need a liner for the hot water tank. And that he (the customer) should pull his head out of his butt, take pictures and sue the SOB from the low life HVAC company. But in the mean time get the damn thing fixed and stop the chimney from deteriorating.
    This has me pissed more than the customer...........

  9. #9
    Join Date
    Mar 2007
    Location
    Toronto
    Posts
    29
    Post Likes

    Condensation

    This is potentially a life threatening situation. Not only is condensate collecting in the chimney but it’s also likely collecting in the vent connector and boiler itself. The condensate is acidic and over time it will oxidize metal. Vent connectors will fall apart and boiler combustion passes will become blocked. This can cause combustion issues in the boilers resulting in the production of carbon monoxide. This will be compounded by a deteriorating chimney.

    A chimney liner is a must and I would suggest a by-pass on the boiler loop to increase the boiler water temperature. This will stop the non condensing boiler from condensing. This will help protect the boiler, vent connector and the chimney liner.

    Good luck.

  10. #10
    Join Date
    Jan 2010
    Posts
    1
    Post Likes

    still learning. dont know what to think

    The G.M. on the job I'm at is certain that the sidewall condensing boiler flue gas is causing an ice damn 30 feet above on a vented eve. 8 feet across from the termination is a 20 foot wall and to the right is another wall 30 feet high. The rest of area open to fresh air. I would think any moisture would be gone within a 10 foot radius. There are also windows above that don't have any condensation on them. Any pro opinions PLEASE?

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •