I built my new home:
1. on an ICF Perimeter wall
2.#" Slab with a 8mm Vapor barrier
3. No Vents
4. Conditioned crawlspace
-
01-13-2010, 07:20 PM #15
not really. that's what i call a poor mans crawl space dehumidifier lol that's what i did at my dads house. i covered the earth with 12mil plastice, and sealed the vents. i didn't insulate the walls, and i use an 8x8 return that i fabricated myself, and i have 4x6 supply. nice and cozy down there summer and winter
If Guns Kill People, Do Pencils Misspell Words?
http://www.youtube.com/watch?v=An2a1...eature=related
Before we work on artificial intelligence why don't we do something about natural stupidity?
http://www.youtube.com/watch?v=nFl0n...ture=endscreen
-
01-13-2010, 07:22 PM #16If Guns Kill People, Do Pencils Misspell Words?
http://www.youtube.com/watch?v=An2a1...eature=related
Before we work on artificial intelligence why don't we do something about natural stupidity?
http://www.youtube.com/watch?v=nFl0n...ture=endscreen
-
01-19-2010, 11:31 AM #17
This is from the Residential 2006 ICC:
R408.3 Unvented crawl space. Ventilation openings in under-floor spaces specified in Sections R408.1 and R408.2 shall not be required where:
1. Exposed earth is covered with a continuous vapor retarder. Joints of the vapor retarder shall overlap by 6 inches (152 mm) and shall be sealed or taped. The edges of the vapor retarder shall extend at least 6 inches (152 mm) up the stem wall and shall be attached and sealed to the stem wall; and
2. One of the following is provided for the under-floor space:
2.1. Continuously operated mechanical exhaust ventilation at a rate equal to 1 cfm (0.47 L/s) for each 50 ft2 (4.7 m2) of crawlspace floor area, including an air pathway to the common area (such as a duct or transfer grille), and perimeter walls insulated in accordance with Section N1102.2.8;
2.2. Conditioned air supply sized to deliver at a rate equal to 1 cfm (0.47 L/s) for each 50 ft2 (4.7 m2) of under-floor area, including a return air pathway to the common area (such as a duct or transfer grille), and perimeter walls insulated in accordance with Section N1102.2.8;
2.3. Plenum complying with Section M1601.4, if under-floor space is used as a plenum.