    Heatilator ND 4236

    WE have a 4 yr old home built with Heatilator ND4236. FP exits on westside of home and is exposed to cold easterly winds. We experience severe cold air leakage from base of unit where air would normally be drawn in to be heated. (From what i understand)

    Builder did remove siding and make repairs/insulate back of unit during our first winter in home. It seemed to help. During winter of 2008-09 we noticed cold air leaking again and sealed off base air supply, secured gas and quite using unit.

    Builder went out of business. Local Heatilator is reluctant to repair as he did not do install. He did suggest removing siding around back of unit, cut out insulation and add bags of vermiculite to seal up outside of Heatilator. He told me, off the record, that Heatilator would advise he to do same.

    House is a ranch with vent coming straight out back of unit horizontally Fireplace sits on cement kickout with plywood base. Ground clearance is approx 5 inches off ground.

    Appreciate any advise. I was told to figure $2500 to remove and reseal. Also read air leakage is always an issue and most builders were not qualified to do proper install. It is getting confusing!

  2. #2
    Join Date
    May 2005
    Location
    Madison, WI
    Posts
    1,078
    Post Likes
    Ok first thing, the vermiculite trick is old, and also violates the clearances of the fireplace and venting and WILL make your house start on fire eventually. Maybe this is why Heatilator would not reccomend it? I suggest not listing to anything that guy says after that stupid suggestion.

    Secondly, make sure the glass on the fireplace is seated properly and clipped on in all for corners, or all three springs acorss the top depending on the glass mount it has.

    If air is not leaking through the glass, it is probably leaking into the chase behind the fireplace due to the walls back there not being built / insulated to proper building codes.

    This has been brought up on this forum amny times.

    http://hvac-talk.com/vbb/showthread.php?t=159965
    http://hvac-talk.com/vbb/showthread.php?t=439952
    http://hvac-talk.com/vbb/showthread.php?t=249702

  3. #3
    Join Date
    Dec 2009
    Posts
    8
    Post Likes
    Thread Starter
    The tip to use vermiculite came from a Heatilator dealer. He did claim Heatilator had suggested same thing in the past. Glad I got a 2nd opinion.

    I have had the glass off and re-installed it and all 4 clips are in place.

    Is it possible that the air could be entering through the air supply for the firebox?

    I see you are in Madison. Ever get to Racine area for work or can you recommend someone who can handle this type of repair? I don't see myself going back to local dealer.

    After builder repaired/re insulated, I thought my issues were resolved because it did seem to be sealed for two winters

  4. #4
    Join Date
    May 2005
    Location
    Madison, WI
    Posts
    1,078
    Post Likes
    The combustion air supply is sealed to the unit, if that was comprimised somehow it could be leaking. Never seen it happen. Some heatilators have an issue if someone starts taking screws out for rear venting, but then goes to top vent and does not put all the screws back, it can leak. I have only seen this once and it was an old GCDC60. I don't think current models have the same setup.

    What dealer did you talk to? Badgerland in Waukesha?

    Did you see any of the work the builder did? Curious if he sealed the insulation with drywall or something on the inside, or did he just add extra insulation?

  5. #5
    Join Date
    Dec 2009
    Posts
    8
    Post Likes
    Thread Starter
    I didn't see repairs but The expediter for Neumann was a good friend and I believe he had installer do what they felt was a superior job. All of the repairs were conducted from outside. They removed sheets of siding and added insulation as necessary and where it made sense.



    I first talked to the retailer in Sturdevant, Alaskan Fireplace I believe is the name.

  6. #6
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    7,434
    Post Likes

    Cool read the old threads given

    ditto on JTP's comments. Anyone recommending packing any kind of insulation around a fireplace is a special kind of idiot and not your friend.

    Note the difference btw insulation and air sealing--two entirely separate issues. Read the threads he linked before going any further.

    Now that this dealer has proven they are idiots, you will need to find someone else for service. JTP knows his stuff and will assist you. I know him personally and he is top notched.

    HTH,
    Hearthman

  7. #7
    Join Date
    Dec 2009
    Posts
    8
    Post Likes
    Thread Starter
    Thanks Hearthman. Glad I found this forum. Now I just need to find someone I can trust to do a proper repair.

  8. #8
    Join Date
    May 2005
    Location
    Madison, WI
    Posts
    1,078
    Post Likes
    Well it is strange that it seemed to not leak air for 2 years. I would first have someone come service the fireplace and check for air leaks there. Before you do have someone come out can try a few things to pinpoint it a little more.

    A quick test you can do though is find the hole where the gas line comes in, stuck your hand or finger through there and see if you can feel a vast temp difference or air flowing from behind the fireplace to inside the house. If it feels cold back there, or there is air flowing into the house from back there its probably the chase walls leaking, and not the fireplace. Be very careful around the sharp metal where the holes are cit out.

    Also you can try another trick. Turn the gas off to the fireplace and then tape a bag over the cap sealing it to the siding. If the cold air stops coming in then its leaking through the venting or the fireplace. If it continues, it is leaking through the chase. I would give it a day or two with the plastic there to let temperatures stabilize.

    I would hate to have you waste money on a building contractor to find out later it was the fireplace that was leaking the air in. If you determine it is leaking through the chase walls, I would wait till after that's fixed to have someone look at the fireplace itself.

  9. #9
    Join Date
    Dec 2009
    Posts
    8
    Post Likes
    Thread Starter
    The gasline is sealed where it comes into through the box. FWIW, the gas line comes in through the bottom and is accessible through the basement. The fireplace is on a kickout where the foundation is built out.

    Will try closing off the cap and get back to you.

  10. #10
    Join Date
    Jul 2007
    Posts
    3
    Post Likes

    Damn neumann

    I have the same issue... same builder.

    Mi ND4236 doesn't get very warm at all. How big should the flames be? And how close should I need to be to feal the heat? Do these come with Concrete logs I could replace with ceramic?

    I am wondering how much is the build quality... is this a good fireplace or should I have low expectations?

    Thanks for the info on alaskan fireplaces... although the guys in lake geneva told me they wouldn't help me either.

    jtp10181 seems to me that you should open a SE location business. Folks up and down the street by me all have similar problems. Shoot if you were to come out I could probably find a half dozen neighbors all wanting the same help. (seriously - I could probably do this we need someone like you)
    Last edited by dougor; 02-12-2010 at 10:12 PM.

  11. #11
    Join Date
    May 2005
    Location
    Madison, WI
    Posts
    1,078
    Post Likes
    Chalky has already contacted me off the forums about doing a repair, so we might be in that area once we slow down a little. We could do 2 or 3 in one day. I have various contact info in my profile.

    Also the Heatilator fireplaces are definitely made well and not a bad fireplace. The brand is geared towards "value". So for the basic "builder" models you get a good fireplace but without a lot of extra features. It should already have fiber-ceramic logs in it.

    Do you get the same cold draft coming in under your fireplace? Or does yours just need service work done?

  12. #12
    Join Date
    Jan 2008
    Location
    Hudson, WI
    Posts
    27
    Post Likes
    check the silicone used to seal the hole were the pilot line, thermopile& thermocouple come thru the firebox. they had some runs that used a different silicone and has been found to get hard and break apart causing air to leak thru that area.

  13. #13
    Join Date
    Dec 2009
    Posts
    8
    Post Likes
    Thread Starter

    Still looking for assistance

    I started talking to Heatilator. They seem quite certain issue is install related.

    I went back out today and pulled the cap off just for my own curiosity. It looked like normal stove pipe on cap where it goes through wall and just presses into pipe coming up from Heatilator.

    FP has a horizontal exit with a 90* down pipe where cap matches up. In looking at various instructions, it generally shows a inner/outer pipe, not the single pipe I saw. Is this normal?

    I found one of the original construction people and he indicated the chases were all drywall finished and insulated. I am beginning to think my issues are related to the vent pipe leaking air.

    Appreciate any info on the pipe for venting as far as type of pipe and any other relevant info.

  14. #14
    Join Date
    May 2005
    Location
    Madison, WI
    Posts
    1,078
    Post Likes
    Its a double wall pipe. The back of the instructions would have some drawings of it.

    You would have to take a picture.

    Usually if the pipe is as wrong as you make it sound the fireplace would not even run.

    Didn't you already try the bag trick, taping a bag over the term cap to see if it would help, and it did not? Taking it a step further, while you have the cap off you can jam some rags in then vent when its cold outside and see if that stops the air coming in. If it does not stop, you have just eliminated the vent (which I think we did once already).

  15. #15
    Join Date
    Dec 2009
    Posts
    8
    Post Likes
    Thread Starter
    I may not have given the bag trick adequate time. The leak is really dependant on winds out of the west directly on to the back of the house.

    What I do have is a single pipe not a double walled pipe per the manual. I found an authorized repair shop locally who is coming out Thursday. We will go from there.

  16. #16
    Join Date
    Dec 2009
    Posts
    8
    Post Likes
    Thread Starter

    Problem solved

    Didn't mean to leave this thread hanging. Long story made short, I called Van's Gas in Kenosha, WI following suggestions from Heatilator. Scott, owner of Van's crawled into the attic and found air paths from attic to fireplace chase. He opened the chase from the outside, did an incredible job of sealing and repairing the chase. All is well and no leaks.

    Anyone from SE WI with a leaking direct vent FP, call Van. Highly recommend.

  17. #17
    Join Date
    Nov 2010
    Location
    Bloomington, In
    Posts
    19
    Post Likes
    Woah! I can't beleive Van is getting shout out on this forum! I agree with Chalky, call Van the man, I can't give the full number but if you look up the area code i think it's (***) 4396710

  18. #18
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    7,434
    Post Likes

    Cool

    If you have single walled pipe on that fireplace shut it down and do NOT burn it as is! That would be an extreme fire hazard. If it has an elbow venting downhill or below horizontal, ditto. Sounds like you may have a construction defect case on your hands. You should have a pro who is familiar with the HL product line perform a Level III internal inspection. I personally know JTP and he would be qualified to perform this inspection. Or you could pay me to fly out and do it.

  19. #19
    Join Date
    Jul 2007
    Posts
    3
    Post Likes

    Thanks

    I am not quite sure if I can figure out the Van mans 262 number but I will definately be giving him a shout tomorrow as my fireplace continues to drive me crazy. Thanks!

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •