Thread: Do York pressure switches have a design flaw?

  1. #1
    Join Date
    Dec 2009
    Posts
    1
    Post Likes

    Do York pressure switches have a design flaw?

    I've got a York Affinity 9.M furnace that was installed (brand new) in my Portland, OR home 3.5 years ago. During three of the four winters I've had it, it has stopped working at least once with the same problem: It flashes three red lights, which is code for "pressure switch stuck open."

    The original installers have been good about coming out here and replacing the pressure switch for free each time, and once they replace the pressure switch, it works fine (until the next time). It hasn't cost me a dime, but it's extremely inconvenient, and it only seems to happen when we're having the coldest and/or windiest weather of the year. I've probably gone through five or six pressure switches in four years.

    I was told that this is due to a defective pressure switch that York uses in their newer furnaces, and that there's nothing to be done about this except replace it when it goes bad. I find that hard to believe (and harder to believe that someone hasn't filed a class-action lawsuit against them by now if it is true). Can any pros out there lend some insight?
    Quick reply to this message Reply  

  2. #2
    Join Date
    Jan 2008
    Posts
    2,904
    Post Likes
    If it is a defective pressure switch, they should put in one that isn't defective. And York doesn't make the pressure switch.
    5 or 6 in 4 years is not right.
    There is some other problem.
    "Hey Lama, hey, how about a little something, you know, for the effort." And he says, "there won't be any money, but when you die, on your deathbed, you will receive total consciousness." So I got that goin' for me, which is nice. - Carl Spackler
    Quick reply to this message Reply  

  3. #3
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Good chance you have a condensate problem.
    Quick reply to this message Reply  

  4. #4
    Join Date
    Jun 2006
    Location
    Hastings, MN
    Posts
    417
    Post Likes
    Agree with Beenthere, I have see on really cold days she is making alot of condensation floods back and gets water in pressure switch. Have him check venting and check furnace condensation draining. Should be done every year on the clean and tune.
    Aint Notin Sweeter, Then A Brand New Heater!!!!!!!!!!
    Quick reply to this message Reply  

  5. #5
    Join Date
    Jan 2009
    Location
    Florida
    Posts
    210
    Post Likes
    sounds more like a defective tech than a defective part
    Quick reply to this message Reply  

  6. #6
    Join Date
    Nov 2009
    Location
    Sacramento, CA
    Posts
    140
    Post Likes
    In agreement with gentlemen above. Condensate drainage problem, not switches.
    Quick reply to this message Reply  

  7. #7
    Join Date
    Dec 2009
    Location
    Buffalo, N.Y
    Posts
    101
    Post Likes

    Thumbs up

    Very recently, I had a similar problem, newer unit, different model, but same manufacturer. Upon arrival to the service call, I learned that the unit (2 years old) was on its 2nd pressure switch. The pressure switch was rated 1.45 in.wc., I measured with a dwyer water tube manometer 1.4 in. differential pressure from draft motor to burner box. I measured 1.6in. from draft motor to atmospheric. The switch would make when disconnected from the burner box port. I inspected the draft motor, primary and secondary heat exchangers, collector box, gaskets, drainage system, intake and vent pipes, and found all to be ok, no loss of integrity. I contacted the factory (not much help), I told them I wanted them to warranty the draft motor even though it ran, eventually they agreed. Installed new motor, now measure 1.55 in. differential between draft motor and burner box. Same pressure switch, furnace works great.
    Quick reply to this message Reply  

  8. #8
    Join Date
    Jan 2009
    Location
    Middle of the Oregon Coast
    Posts
    205
    Post Likes
    PDX - York does have a problem with their pressure switches, but from what I am being told, they have it worked out. The pressure switch closes, but the contacts of the electrical portion get pitted and won't conduct the signal any more. There is also a bulletin out regarding the "routing" of the tubing going to the pressure switch. If your tech has any problems or doesn't know about the bulletin, just tell him to "call David" from York - this may take a few minutes due to the fact he is very busy, but he will return a voicemail. Any other problems, contact me through this board.
    The Lord must love stupid people or he wouldn't have made so many.

    Why is it that when I am in a hurry, everyone else on the road goes 15 MPH under the speed limit?
    Quick reply to this message Reply  

  9. #9
    Join Date
    Sep 2008
    Posts
    58
    Post Likes
    I had similar problem with my Luxaire FL9C during November and again in December last year. Dealer had called February 19th (this year) to say that a new tech bulletin had just been issued. Here is a quote from the note I made after dealer was here to fix it: "new pressure switches to deal with silicone contamination from the hoses going to the switches that was causing the switches to not make electrical contact when closed". Have had no problem since, including day last week when we had 50 MPH winds. Perhaps one of the Luxaire/York/Coleman guys can find the bulletin?
    Quick reply to this message Reply  

  10. #10
    Join Date
    Nov 2008
    Posts
    1,673
    Post Likes
    Quote Originally Posted by PDXhomeowner View Post
    I've probably gone through five or six pressure switches in four years.

    I was told that this is due to a defective pressure switch that York uses in their newer furnaces,
    They would have fixed a design defect by now.
    Quick reply to this message Reply  

  11. #11
    Join Date
    Jan 2009
    Location
    Middle of the Oregon Coast
    Posts
    205
    Post Likes
    They would have corrected it in the factory, but the ones in the field are "fix on fail".
    The Lord must love stupid people or he wouldn't have made so many.

    Why is it that when I am in a hurry, everyone else on the road goes 15 MPH under the speed limit?
    Quick reply to this message Reply  

  12. #12
    Join Date
    Dec 2009
    Posts
    2
    Post Likes

    I had the exact same problem! Just got mine fixed!

    I have been struggling for a week along with my HVAC guy to figure out what was wrong with my York. I had the exact same symptoms as PDX...furnace 3.5 years old, and it kept going to the 3-flash, pressure switch stuck open. Every once in a while it would give me a 6 flash or an 8 flash, but they all pointed to the pressure switch. The HVAC guy even replaced the pressure switch last week, but the problem persisted.

    I woke up at 4:30 this morning and the house was 59 degrees (Minnesota). I started turning the furnace off and on trying to override the failure just to get the house warmed up and that was when I got online and found this discussion. I appreciated some of the good suggestions, but I can say that we are now 100% sure we have fixed my problem and I wanted to share it.

    I have had a field tech coming almost every day for the last week and he just hadn't cracked the nut, so this morning the owner of the firm came out too. What the owner knows (because I have known him for years), that the field tech and you all don't know, is that I have a 2 year old boy who likes to be a stinker. The owner showed up and didn't even bother ringing the bell. Instead he walked to the back of the house, pulled the PVC venting loose at the first corner where it came out of the house, and the problem was solved. My boy had been dropping Class V rocks down the vent all summer and it was choking off the intake! It would be like trying to run a marathon with a mouthful of marbles!! Glad to have the problem solved and thought I would share it with all of you. Enjoy.
    Quick reply to this message Reply  

  13. #13
    Join Date
    Dec 2009
    Posts
    2
    Post Likes

    By the way

    By the way, I realize most of the pros responding to this discussion would probably check the vent elbows (see my previous response), but I posted my example for any other amateurs and DIYers out there that might be trying to figure something like this out for the first time.
    Quick reply to this message Reply  

  14. #14
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,182
    Post Likes

    Cool

    Quote Originally Posted by NotGettingSleep View Post
    I have been struggling for a week along with my HVAC guy to figure out what was wrong with my York. I had the exact same symptoms as PDX...furnace 3.5 years old, and it kept going to the 3-flash, pressure switch stuck open. Every once in a while it would give me a 6 flash or an 8 flash, but they all pointed to the pressure switch. The HVAC guy even replaced the pressure switch last week, but the problem persisted.

    I woke up at 4:30 this morning and the house was 59 degrees (Minnesota). I started turning the furnace off and on trying to override the failure just to get the house warmed up and that was when I got online and found this discussion. I appreciated some of the good suggestions, but I can say that we are now 100% sure we have fixed my problem and I wanted to share it.

    I have had a field tech coming almost every day for the last week and he just hadn't cracked the nut, so this morning the owner of the firm came out too. What the owner knows (because I have known him for years), that the field tech and you all don't know, is that I have a 2 year old boy who likes to be a stinker. The owner showed up and didn't even bother ringing the bell. Instead he walked to the back of the house, pulled the PVC venting loose at the first corner where it came out of the house, and the problem was solved. My boy had been dropping Class V rocks down the vent all summer and it was choking off the intake! It would be like trying to run a marathon with a mouthful of marbles!! Glad to have the problem solved and thought I would share it with all of you. Enjoy.
    Very funny. I have seen similar things before. IT is always the last thing you think of.
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY
    Quick reply to this message Reply  

  15. #15
    Join Date
    Oct 2006
    Location
    The Beach
    Posts
    1,025
    Post Likes
    Also check the grade on the vent piping to make sure there is no condensate or any other material in the piping.
    Blue Fox
    Quick reply to this message Reply  

  16. #16
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    If the tech had used a manometer, he would have seen the vent was the problem, and not the switch.
    Quick reply to this message Reply  

  17. #17
    Join Date
    Jul 2009
    Posts
    3
    Post Likes

    SERVICE LETTER

    SIMILAR SWITCHES ON LUX,COLEMAN.

    SERVICE INFORMATION
    Unitary Products
    5005 York Drive
    Norman, Oklahoma 73069
    1/8778747378
    Date: February 5, 2009 YS00209
    Revised
    To: All York Distributors
    All York Branches
    All Field Service Supervisors
    Subject: Pressure Switches PC9, PM9
    We have received several product reports regarding pressure switch problems on the 40”
    modulating 95% furnaces. (Switch P/N S102435308000/
    SAP# 157719 upflow models &
    S102435324000/
    SAP# 160209 downflow models)
    Investigation into these issues and analysis of field returned switches have shown that the
    fault code 3 is caused by high contact resistance on the electrical contacts within the
    pressure switch. On each ignition cycle, the modulating furnace control ramps the draft
    inducer blower up and down and verifies the pressure sensor and switch operation by
    comparing the switch opening and closing points, as measured by the pressure sensor, to
    the proper switch set point for that furnace model. If the electrical contacts within the
    pressure switch body become contaminated with a foreign material, the switch may close
    mechanically but may not close electrically at the calibrated set point, causing the control
    to detect a pressure switch that is open when it should be closed. This will result in a 3flash
    error code, and the furnace control will not continue the ignition sequence.
    To address this problem, the switch supplier has made a recent change to the switch
    construction to add an industrial contact lubricant that prevents contamination from
    adhering to the electrical contact surfaces. Testing has shown that this makes the contacts
    many times more resistant to contamination by foreign substances. Pressure switches
    with code dates of 0309 (third week of 2009) will have this new construction. Source 1
    should begin to have a limited supply of the new switches available for shipment by
    February 6 th .
    The contact contamination problem will not affect any of the NG33 models, even those
    without the contact lubricant on the pressure switch contacts. The contamination on the
    contacts is usually silicone carbide, the source of which is the silicone hose connected to
    the switch. Silicone molecules outgas from the hose and migrate to the switch contacts,
    eventually affecting the electrical connection. On the NG33 models, which do not have
    closed burner boxes, there is no silicone hose on the side of the pressure switch in which
    the contacts are located, and so there is no direct source for silicone contamination. The
    problem will also not affect previous singlestage
    or twostage
    models, since those
    models do not have pressure sensors that compensate for vent length and firing rate so
    they always provide a pressure level that insures the contacts are cleaned mechanically on
    each cycle.
    This YS letter will provide a replacement pressure switch and one hour labor at the
    dealers registered DOA labor rate. Due to the nature of this issue, we recommend that the
    dealers replace the switches now, instead of waiting for them to fail. Make sure you
    reference the YS letter number when filing claims for this issue.
    For any units in distributor inventory, this YS letter will allow for replacement of the
    pressure switch along with a fair and reasonable allowance. Contact Mark Freund at 4054196609
    for prior authorization to submit the billing for reworking your inventory.
    For repair parts in distributor inventory, contact your Source 1 account representative for
    a Return Authorization of switches with code dates prior to 0309.
    Mark Freund Robert Cabrera
    Mark Freund Robert Cabrera
    Manager, Residential Field Service Director, Indoor Products Engineering
    Quick reply to this message Reply  

  18. #18
    Join Date
    Jan 2010
    Posts
    24
    Post Likes
    Venting (length, pitch, size and amount of elbows) should be checked. Condensate drain should be checked. No way that many pressure switches goes out in such a short time frame. Tech. should also check and make sure that the intake is not pulling the exhaust when the pvc is on the outside of the house. I have seen people install intakes where they are facing down into snow.
    Quick reply to this message Reply  

  19. #19
    Join Date
    Jul 2009
    Posts
    3
    Post Likes

    SERVICE INFO YS-002-09

    SEE MY ABOVE POST. THIS IS A SERVICE LETTER FROM YORK ABOUT SPECIFIC PRESSURE SWITCHES ON CERTAIN MODELS THAT CAUSE ISSUES AND WHY. I RECENTLY ALSO FOUND THE SAME PROBLEM ON A HI END COLEMAN. THE TRICK IS TO CHECK THE PRESS SWITCH PART NUMBER AND CHECK IT AGAINST THIS LETTER. ALSO CHECK THE DATE CODE ON THE SWITCH.
    Quick reply to this message Reply  

  20. #20
    Join Date
    Jan 2010
    Posts
    24
    Post Likes
    Anyway that you could email this to my email. My company does deal with their products and I would like to talk to the MFG rep guru about this the next time that I see him.
    Quick reply to this message Reply  

Page 1 of 4 1234 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •