Results 1 to 5 of 5

Thread: JCI BACnet

  1. #1
    Join Date
    Jul 2009
    Location
    Charlotte, NC
    Posts
    423
    Post Likes

    JCI BACnet

    I've got a co-worker working with JCI BACnet and is having a problem. The system is controlling humidity on an air handler, and the setpoint is 35%. He can go in and change the setpoint from the graphics to lets say 50%, and at random times, the setpoint changes back to 35%, He's also went in and changed the default value to 50%, and the problem still persist. Anyone have an idea of whats causing this? He wants me to go in and take a look, but the JAVA app has taken almost an hour to download remotely. Just figured I'd hit the forum up for some insight. Thanks!

  2. #2
    Join Date
    Aug 2009
    Posts
    2,457
    Post Likes
    I have a feeling that people are going to have to know exactly what model these controllers are in order to offer suggestions.

  3. #3
    Join Date
    Jul 2009
    Location
    Charlotte, NC
    Posts
    423
    Post Likes
    Thread Starter
    I got it figured out. It was a damn reset schedule. These were FEC's by the way.

  4. #4
    Join Date
    Dec 2005
    Location
    San Jose, CA
    Posts
    465
    Post Likes
    Actually there is a patch for version 4.1 I know the latest is 4.1.0.45
    I think but I know for sure there is a patch that addresses bacnet issues.

  5. #5
    Join Date
    Oct 2008
    Location
    Twin Falls, ID
    Posts
    401
    Post Likes
    There is another patch past the 4.1.0.45. The latest version brings it up to 4.1.2.09

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.