I've got a co-worker working with JCI BACnet and is having a problem. The system is controlling humidity on an air handler, and the setpoint is 35%. He can go in and change the setpoint from the graphics to lets say 50%, and at random times, the setpoint changes back to 35%, He's also went in and changed the default value to 50%, and the problem still persist. Anyone have an idea of whats causing this? He wants me to go in and take a look, but the JAVA app has taken almost an hour to download remotely. Just figured I'd hit the forum up for some insight. Thanks!
-
12-09-2009, 12:02 PM #2
Removed by Admin- No Return
- Join Date
- Aug 2009
- Posts
- 2,459
I have a feeling that people are going to have to know exactly what model these controllers are in order to offer suggestions.
-
12-09-2009, 05:02 PM #3
I got it figured out. It was a damn reset schedule. These were FEC's by the way.
-
12-10-2009, 01:30 AM #4
Actually there is a patch for version 4.1 I know the latest is 4.1.0.45
I think but I know for sure there is a patch that addresses bacnet issues.
-
12-10-2009, 05:53 AM #5
Regular Guest
- Join Date
- Oct 2008
- Location
- Atlanta, GA
- Posts
- 115
There is another patch past the 4.1.0.45. The latest version brings it up to 4.1.2.09