    3 phase scroll locked up.

    I had a 3 phase scroll locked up on me. Before I condemed it, I reversed the rotation and got it to run backward. Moved the leads back and it ran fine. Has anyone come across this, or is it common knowledge to do this.

  2. #2
    Join Date
    Jan 2009
    Location
    Indiana
    Posts
    3,228
    Standard 3 phase quick fix...but u still have an issue...why did it lock up in the first place

  3. #3
    Join Date
    Mar 2007
    Location
    State of Confusion
    Posts
    1,174
    Quote Originally Posted by yellowirenut View Post
    Standard 3 phase quick fix...but u still have an issue...why did it lock up in the first place
    agree. There's probably internal damage. They will probably call you back friday at 1pm and want you to install a new compressor.

  4. #4
    Join Date
    Apr 2006
    Location
    Phoenix
    Posts
    17
    Thank you for the reply. I did inform the customer that this was a temp fix and there could still be issues. with thier compressor.

  5. #5
    Join Date
    Dec 2009
    Location
    Fort Worth, Texas
    Posts
    142
    unit probably flooding. Anytime you have a locked up compressor you should check the subcooling,superheat and pressures.

  6. #6
    Join Date
    Dec 2009
    Location
    Dallas
    Posts
    15
    What type of unit is the compressor in? More info

  7. #7
    Join Date
    May 2009
    Location
    Bardstown, KY
    Posts
    83

    CCH

    Check the crankcase heater. Oil foaming on startup washes the bearings and shortens life of compressors.

  8. #8
    Join Date
    Jul 2009
    Posts
    56
    just had a 7.5 ton trane rtu do the same thing.... after futher checking
    the control circuit was calling for both heat and cool.... on/off sequence
    fried the compressor.

  9. #9
    Join Date
    Jul 2000
    Location
    Treasure Coast/Florida
    Posts
    9,749
    The initial "no-start" may have caused by axial sealing of the scrolls due to a higher pressure on the suction side than on the discharge side. Here's an excerpt from a scroll replacement guide by Copeland Europe:
    Rapid charging on the suction side of scroll compressors can occasionally result in a temporary no-start
    condition for the compressor. The reason for this is that if the flanks of the spirals happen to be in a sealed
    position, rapid pressurization of the low side without opposing high side pressure can cause the spirals to seal
    axially. Consequently, until the pressures eventually equalize, the spirals can be held tightly together, preventing
    rotation. The best way to avoid this situation is to charge on both the high and low side simultaneously at a rate
    which does not result in axial loading of the spirals.
    Here's a link to the page:
    http://www.ecopeland.com/literature/...idelines_0.pdf