    rapid zone scheduling ugh!

    i have been tasked with setting up lonstation and adding 15a's for scheduling.
    in order to avoid hacking the rapid zone program and having to install a gang of 15a's (limited to 18 Schedule assignments) i came up with a bright idea.

    schedule a digital output through the ss loop and and have the do open and close the time clock input. genius. well i think the timeclock di doesn't like the 15c do. im guessing triac issues. any way around this without installing a bunch of relays ? maybe a resistor ?
    IV IV IX

    use your head for something other than a hat rack.......Gerry


    We have freedom because somebody fought for it.
    We keep it because we are willing to fight for it.
    We lose it because we are not willing to fight for it.

  2. #2
    Join Date
    Sep 2007
    Posts
    71
    Post Likes
    If you have LonSpec you could do a project backup from the network screen in RapidZone then restore to LonSpec. Go to Network, Refer Points. Select the XL15A as the source controller and TOD Event 1 as the source point. Select all zone controllers that couldn't be directly scheduled in the destination controllers and nviTodEvent as the destination point.

    Beats rewiring...