    I Have 3 15 ton cond air-cooled cond. units all 6 months old which all have 1 inch stroke low ambient pistons controlling the damper in the discharge duct. All units are having a problem running in cold weather by tripping on low pressure. All circuits have low press bypass timers. Does anyone think switching to a 2 inch stroke piston would be more responsive. Thanks for any responses.

  2. #2
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,635
    your profile doesn't give any indication why you would need this kind of info.
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  3. #3
    Join Date
    Dec 2007
    Location
    woodhaven ny
    Posts
    4
    I guess I never spent much time while registering to update any profile. I'm a service tech in NYC

  4. #4
    Join Date
    Mar 2008
    Location
    NY NY
    Posts
    181
    Assuming that your condition is a result of low head pressure, you may want to go with a motorized head pressure control system. I thought the old mechanical damper controls we obsolete.

    You can talk to West at (212) 947-3100 for the details.


    Regards
    Local 30 New York, New York Operating Engineer

  5. #5
    Join Date
    Dec 2007
    Location
    woodhaven ny
    Posts
    4
    Thanks but we installed this equipment and I can't make any big modifications. I'd much rather use a pressure transducer with an actuator in the damper but I was wondering if a 2" stroke would be more responsive. The cond fan motor is 5 hp. I'll try Wes at industrial tomorrow. Thanks.

  6. #6
    Join Date
    Mar 2008
    Location
    NY NY
    Posts
    181
    I’m fairly sure the pricing will be similar for the motorized controls.
    Local 30 New York, New York Operating Engineer

  7. #7
    Join Date
    Nov 2001
    Location
    Long Beach New York
    Posts
    596
    I had a couple giving me grief last winter over at the brooklyn piers, the dampers were not closing completely on shut down, so the head would never get a chance to build up on start. Those were Carrier SCAV'S with after market low ambient dampers. After adjusting the dampers they were o.k.

  8. #8
    Join Date
    Dec 2007
    Location
    woodhaven ny
    Posts
    4
    Thanks for the suggestions. Just tried the motorized actuator with a press transducer but the motor wouldn't respond fast enough causing my head and back pressures to drop. Going to get drives with transducers that should do it.

  9. #9
    Join Date
    Mar 2008
    Location
    NY NY
    Posts
    181
    Stanyoung,

    If you are using the Belimo AMQB 24 actuator the stroke timming is adjustable on the motor.


    Regards
    Local 30 New York, New York Operating Engineer

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event