XL-10's go occupied when comm is lost.
I am installing a Jace to integrate about a dozen XL-10 controllers, there is an XL-15 on the network that I am going to replace with a Distech Lon controller. Should I replace the XL-15 first or install the Jace? Sounds like the XL-15 does all the schedules for the other controllers so I am worried they will crap out. But I might have the same result if I install the Jace first. Any ideas? Thanks!
XL-10's go occupied when comm is lost.
I'm going to leave the building manager and plant manager controllers in and learn them so I can see the bindings. Then rip them out later.
So I got around to doing this today, went well but every time I delete a binding, it reappears. I did a quick learn,commissioned all of the devices, and then did a bind from the Lon link manager. When I delete the OA broadcast from the plant controller, it continues to write to the point. If I relearn the plant controller the bindings reappear. What am I doing wrong? Thanks guys.