    Honeywell LCBS to NiagaraAX

    I am installing a Jace to integrate about a dozen XL-10 controllers, there is an XL-15 on the network that I am going to replace with a Distech Lon controller. Should I replace the XL-15 first or install the Jace? Sounds like the XL-15 does all the schedules for the other controllers so I am worried they will crap out. But I might have the same result if I install the Jace first. Any ideas? Thanks!

  2. #2
    Join Date
    May 2009
    Location
    in the present
    Posts
    94
    Post Likes
    XL-10's go occupied when comm is lost.

  3. #3
    Join Date
    Mar 2014
    Location
    Pittsburgh, PA
    Posts
    278
    Post Likes
    Thread Starter
    I'm going to leave the building manager and plant manager controllers in and learn them so I can see the bindings. Then rip them out later.

  4. #4
    Join Date
    Mar 2014
    Location
    Pittsburgh, PA
    Posts
    278
    Post Likes
    Thread Starter
    So I got around to doing this today, went well but every time I delete a binding, it reappears. I did a quick learn,commissioned all of the devices, and then did a bind from the Lon link manager. When I delete the OA broadcast from the plant controller, it continues to write to the point. If I relearn the plant controller the bindings reappear. What am I doing wrong? Thanks guys.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •