    Quote Originally Posted by sysint View Post
    JustJohnson- Ask yourself which method is more susceptible to inaccuracy over distance? (0-10 or 4-20)
    --- now somebody here will tell you I'm just sales... but ignore that guy for now.
    It's true. But it's TECHNICAL sales.
    New Hampshire
    now maybe I'm in for a lesson here - but aren't the dipswitch/jumpers on some controllers just adding/subtracting the resistor into the electrical circuit before the A/D converter just like I add an external resistor? All controllers actually measure voltage - even when using a resistance temp sensor - they send out a reference voltage and the returning voltage calculates to a resistance which equals a temperature. I've not had accuracy problems with mA devices with an external resistor at the controller. Now a device that generates a voltage signal at the device over long runs (>200+ feet) I agree with you you get resistance added because of the wire run and your voltage signal is skewed. Perhaps I'm missing something but that's the way I've always done it and I don't have problems with it.
    Aug 2009
    JJ- You are 100% correct.
    Everyone on this board knows that a current signal won't degrade since it's a closed loop system.
    Your assumptions about resistors are right on the money- You can add them yourself or switch/jumper them in if the manufacturer spent the extra 15 cents to make the input selectable. Either way there is no difference electrically.