    Hean & Glo CERONA-42

    I have a customer that has a GEM-42 gas fireplace made by Heat & Glo that ignites sometimes, and sometimes not. When it does not lite, there is no gas or spark to the pilot.

    I've verified 110VAC to the junction box and that there is 2.9v going into the module from the transformer. The wall switches will not turn on the unit, but the local switches sometimes allow the system to operate. Would the module, if bad, operate sometimes?

    I have the troubleshooting tips from the installer's manual, but that isn't much help. Where can I obtain a troubleshooting flow chart with voltages at the different terminals? It may be a wiring issue because it is a rat's nest of wiring under there.

    Feel free to email me at

    Thanks guys !!!
    Last edited by beenthere; 12-02-2009 at 06:55 AM. Reason: Removed email address

  2. #2
    Join Date
    May 2005
    Location
    Madison, WI
    Posts
    1,078
    Is it a GEM or a Cerona?

    That GEM unit should have an upgrade kit applied to it which has a timer delay built in for the burner ignition. The pilot must be on 3-5 mins before the burner will ignite.

    Check your email

  3. #3
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    393
    The ID tag says GEM, but I didn't find any info on the GEM and when I searched GEM, the results came back cerona. I didn't know there was a difference.

    The upgrade, is that in reference to the recall that was issued? I am not sure if this unit has been upgraded yet.

    Got your email and replied, a 1000 thanks !!!

  4. #4
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,594
    Put your email address in your profile, not in post.
    Bots scan for them. And slow the system down once they find one.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #5
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    6,277

    Cool

    You can contact HG Tech Support with the serial number of that unit and they can tell you if it was officially converted under the recall or not. This kit includes reinforcement for the glass front as well as the delay on make timer function. There is a special sticker that should be present down below.

    Hearthman

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event