    Temp output during defrost

    I got a reading of about 65 deg. from my vent during a defrost cycle. Is this an acceptable temp? Seems a little cold to me.

  2. #2
    Join Date
    Dec 2003
    Location
    Citrus County, Florida
    Posts
    1,231
    what size heat strips do you have? Size of the Air handler?
    Doug

  3. #3
    Join Date
    Jan 2008
    Location
    Lehighton, Pa.
    Posts
    171
    It's a 4 ton with 10kw

  4. #4
    Join Date
    Dec 2003
    Location
    Citrus County, Florida
    Posts
    1,231
    seems a little cold. Pull amp draw to see if all strips are connected and functioning. I've seen units installed with undersized wire and breakers. The installer would disconnect some of the strips so you may have 10KW but only 5 or 7kw connected.
    Doug

  5. #5
    Join Date
    Mar 2006
    Location
    The South
    Posts
    1,843
    jeepgrady

    I think the other question that should be asked is "why are you even having a defrost call" for the SC coastal area.

    what was outside temp and humidity when defrost call started?

    time defrost or demand defrost?

    TD

  6. #6
    Join Date
    Mar 2007
    Location
    Myrtle Beach, SC
    Posts
    2,850
    Bob,

    You have demand defrost with your Lennox XP-16. 65 degrees seems about right with a 4 ton and 10 KW strips. I have had 2 other calls on defrost already today. It was 37 degrees when i got up this morning, it is normal to have defrost during those conditions.

    Kevin
    Remember, Air Conditioning begins with AIR.

  7. #7
    Join Date
    Jan 2008
    Location
    Lehighton, Pa.
    Posts
    171
    Thanks Kevin. I know about the demand feature. It just seemed 65 was a little chilly when in defrost. If you say it's OK, that's good enough for me.

  8. #8
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    31,530
    You have 48K cooling and 34K heating. Cool air would be expected.

  9. #9
    Join Date
    Sep 2002
    Location
    I don't know
    Posts
    2,888
    That's a minimal amount of back heat for a 4 ton HP - I hope you're in a hot climate.

  10. #10
    Join Date
    Jan 2008
    Location
    Lehighton, Pa.
    Posts
    171
    Read my signature. I'm in SC.

  11. #11
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    5,255

    Question dT =?

    Quote Originally Posted by jeepgrady View Post
    I got a reading of about 65 deg. from my vent during a defrost cycle. Is this an acceptable temp? Seems a little cold to me.
    Supply & Return can NOT be the same if the strips are working.
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art".

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  12. #12
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,212
    Quote Originally Posted by BaldLoonie View Post
    You have 48K cooling and 34K heating. Cool air would be expected.
    yep




    you're going to have cool draft during defrost..................
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  13. #13
    Join Date
    Mar 2007
    Location
    Myrtle Beach, SC
    Posts
    2,850
    Quote Originally Posted by dan sw fl View Post
    Supply & Return can NOT be the same if the strips are working.
    They can if both the heat and cool are on at the same time, which is the situation during defrost.
    Remember, Air Conditioning begins with AIR.