Not sure what you mean. I'm referring to this: Vykon HVAC. It is Jace2 and 6 (I believe they are available in US) with special jar modules.
-
11-30-2009, 11:27 AM #15
So how are you communicating between the JACEs? LON, MODBUS, or through the LAN? Just curious. Thanks.
-
12-01-2009, 05:26 AM #16
I have seen it done twice (by the same company) with R2 Jace with onboard IO and also Honeywell LON IO in the larger panels. Lon was also used for the VAVs and also Modbus for Metering. Small fixed application LON IO for tenants metering and miscellaneous monitoring/control.
It worked well and I assume is cost effective otherwise they would not have used this approach.gnomethang
_______________________________________________
"Once men turned their thinking over to machines in the hope that this would set them free. But that only permitted other men with machines to enslave them."
- The Reverend Mother Gaius Helen Mohiam
-
12-06-2009, 12:26 AM #17
New Guest
- Join Date
- Dec 2009
- Posts
- 3
A other option
I have done it a few time. No problem.
You could also consider the honeywell Spyder. Smaller controllers, availables with BACnet or Lonwork network and they are program with Workbench. They are Niagara AX base controller.
Using Spyder ctrl's network to a WEB-201 (Jace-2) would cut your price even more, with the same benefit of using only Jace-2.
-
12-06-2009, 12:03 PM #18
-
12-06-2009, 12:42 PM #19
Regular Guest
- Join Date
- Nov 2007
- Location
- Phoenix, AZ
- Posts
- 256
Jace I/O
I agree and if you have a java programmer around you can do it in baja. I have developed a generic ahu block for 90 % of the ahu's we do. I use th jace for this all the time. I use cat 6 or lon depending on whats going on.
Remember that if you are going to use I/O, it needs to be on the jace when its first set up and your good to go.
If you write a generic ahu program (java or block) you can use it over and over again. Set up time becomes short, hours drop and more money made.
Greg
-
12-06-2009, 02:33 PM #20
I wouldn't plan on using a WEB-201 if you need access to the programming tool after installation. See the HW Spyder compatibility matrix, I don't think HW supports the tool on a 201.
It could be done if you bring them in as dynamic devices, but you'd lose the ability to replace a controller remotely.
-
12-09-2009, 08:21 PM #21
Professional Member
- Join Date
- Jan 2009
- Location
- Massachusetts
- Posts
- 181
New Spyder tool will allow to program on the JACE. It doesn't take any additional memory compare to dynamic device. The program is loading to the memory only when you see wire sheet and unloading as soon as you switch to another one.