Thread: Jace as a AHU conroller
-
11-27-2009, 07:51 AM #1
Professional Member
- Join Date
- Mar 2008
- Posts
- 103
Jace as a AHU conroller
Thanks in advance for any opinions. Still new to the AX product.
Are many people using a Jace with I/O as a stand alone AHU controller.
Have a job oprtunity that requires custom AHU's with a lot of downstream zone control (not VAV). Site would have numerous similar setups, with Jace's
networked together.
Thanks again
b-man
-
11-27-2009, 08:11 AM #2
Wow! That sounds like an expensive AHU controller. Why would you want to use a Jace as a stand-alone controller when there will be several other Jaces on the same project? Do you have access to any other control lines?
"Controls is a lifestyle not a job" -klrogers
-
11-27-2009, 09:04 AM #3
Professional Member
- Join Date
- Jun 2009
- Location
- StL, MO
- Posts
- 532
-
11-27-2009, 09:44 AM #4
b-man is probably talking about a jace2, and with expansion i/o, price per point is pretty unbeatable. I think if he has a high number of zones, it makes sense.
-
11-27-2009, 12:37 PM #5
Professional Member
- Join Date
- Jan 2008
- Location
- Near Philly
- Posts
- 382
I've seen it done. Two items really popped out. The wire sheet was incredibly ugly, and no local display. I priced a similar situation, the hardware point cost was nearly identical as opposed to a standard field controller with expansion modules. The programming time will be high, every little step is custom.
-
11-27-2009, 06:36 PM #6
Professional Member
- Join Date
- Sep 2007
- Posts
- 132
-
11-27-2009, 06:39 PM #7
Professional Member
- Join Date
- Sep 2007
- Posts
- 132
-
11-27-2009, 07:13 PM #8
Sure, if you had one as a stand-alone on a project.
Why, have multiple Jaces when you only need one Jace 6 to handle the web interface, graphics, alarms and trends. I just dont see the advantage to installing a Jace on every piece of equipment in the house."Controls is a lifestyle not a job" -klrogers
-
11-28-2009, 04:34 PM #9
Professional Member
- Join Date
- Sep 2006
- Location
- EU
- Posts
- 161
Just FYI Tridium Europe sells Vykon HVAC system: a Jace, which controls AHUs, cooling/heating plants etc through inexpensive Modbus IO. All programming and configuration is done with wizards (no real programming) VERY quick and simply.
-
11-29-2009, 08:13 AM #10
I use them all the time for retro fits, just replaced (11) 8x8 Staefa with 4 Jace20s (Lynxspring's PC-1000). I Also use them for boiler and chiller plants. NO issues what so ever. If you have tons of logic then make sure you use a 60.
I have analyzed price per point and I am very competitiveIntelli-Building = Less Stress, commissioned with diligence!
-
11-29-2009, 08:24 AM #11
1-Ugly wire sheet is result of sloppy programming.
2-I can program faster in a Jace than any other environment, except basic. Utilizing saved .bogs, cut paste, custom program objects, and search and replace. The secret to ANY programming is BUILD LIBRARY'S of code or objects, re-use,re-use, re-use.
3-Don't know where u buy your Jaces but my price per point smokes!
4-I have a Jace display I use all the time! Remove cover, add option card, plug in display, snap on new LCD cover presto done! (Well add the lcd extensions first)Intelli-Building = Less Stress, commissioned with diligence!
-
11-29-2009, 08:28 AM #12
-
11-29-2009, 09:21 AM #13
Professional Member
- Join Date
- Mar 2008
- Posts
- 103
Jace as a AHU controller
Thanks for all the input!
The zones could add up to 75-100 points (I/O) plus the points of the AHU.
Customer must have access to the programming tool. This solution would not only allow them access to programming of the AHU/zones, but be able to use the same software platform for graphics, trending and alarming.
Each AHU must be standalone controller, in case of a crash, no other AHUs will go down, "Critical Areas".
Cost is always an issue, but in this case reliability and expandability are the main issue.
b-man


Reply With Quote