  1. #14
    Join Date
    Jan 2008
    Location
    windy city
    Posts
    4,401
    basically the same as the above. 4# is plenty of pressure, altough i have one r11 hr i bump it up to 20, with the burst disc removed. you do not see bubbles, you don't have a leak. i have several leak detectors, use the one closest to the door, including halide, which is tough because i'm color blind

  2. #15
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,577
    Quote Originally Posted by CaptJackSparrow View Post
    Sorry Graham I have a different opinion I think hot water leak checking is %$#@^%! I have caused more leaks with hot water than I can stand. We went to chillers with no purge time, hook up the hot water and boom, leak rates up, we go back to the job and theres a big leak on the terminal board or somewhere. Usually a flat gasket! We do agree that the purge is the best leak detector. If it aint purgen! dont leak check it! Just verify purge operation. If you do recover the charge you get to do a leak test even better than a purge, thats is a vacuum test. When you leave the job you know for a fact how tight the machine is. I dont mind using hot water on some machines like 19ds, they have the paper/asbestos gaskets and dont seem subject to leaking after hot h20. I have 1990 CVHE that has about 500 mins of pumpout time, That came from my first hot water leak check on it. Caused the term board to leak. It has never been leak checked again and is tight. I have other stories but just to give my two cents own the matter, I think the hours padded into the annuals to leak check is BS. I wish the industry would change and stop leak checking non leaking chillers, also change the scope and price to reflect that! We at my "old job" always charged for the leak check but seldom performed the leak check. Which can get me off on another soap box so i will shut up while i am ahead!
    Give me a reason give it a leak test agree with all of the above.
    Arguing with your Boss is like wrestling with a pig in
    mud.
    After a while you realize that while you are getting
    dirty, the pig is actually enjoying it.

    It is not exactly cheating, I prefer to consider it
    creative problem solving.

    25 years ago we had Bob Hope , Steve Jobs , and Johnny Cash today we have no Hope no Jobs and no Cash !
    I can fix broke but i can't fix stupid !

  3. #16
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    1,860
    Originally Posted by CaptJackSparrow
    Sorry Graham I have a different opinion I think hot water leak checking is %$#@^%! I have caused more leaks with hot water than I can stand. We went to chillers with no purge time, hook up the hot water and boom, leak rates up, we go back to the job and theres a big leak on the terminal board or somewhere. Usually a flat gasket! We do agree that the purge is the best leak detector. If it aint purgen! dont leak check it! Just verify purge operation. If you do recover the charge you get to do a leak test even better than a purge, thats is a vacuum test. When you leave the job you know for a fact how tight the machine is. I dont mind using hot water on some machines like 19ds, they have the paper/asbestos gaskets and dont seem subject to leaking after hot h20. I have 1990 CVHE that has about 500 mins of pumpout time, That came from my first hot water leak check on it. Caused the term board to leak. It has never been leak checked again and is tight. I have other stories but just to give my two cents own the matter, I think the hours padded into the annuals to leak check is BS. I wish the industry would change and stop leak checking non leaking chillers, also change the scope and price to reflect that! We at my "old job" always charged for the leak check but seldom performed the leak check. Which can get me off on another soap box so i will shut up while i am ahead!

    Agreed dont get me wrong" if it aint purgin it aint leakin" as long as the chiller gets some off time to be sure its not a high side leak . But there are customers who say "I paid for a leak test so I want it a leak test " So I give them a "courtesy" leak test to appease them .
    You are better off doing thorough purge maintenance and spending time checking all the flat gasket joints once a year to check if they are tight . Particularly motor cooling lines and economizer vent lines etc.
    The 64 roars to life Whoo hoo ...shes a rolling chassis .
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

  4. #17
    Join Date
    May 2001
    Location
    Western Wa
    Posts
    1,761
    If the unit has a rupture disk, I wouldn't go above 5 psi.
    God Bless the USA

  5. #18
    Join Date
    Nov 2007
    Location
    DownUnder
    Posts
    33
    Try the purge itself, for leaks. You can also have a go at running the chiller with the purge valved off and isolated see if it stays the same or gets worse. I have had some trouble in the past with the connections on the purge driers and the valves themselves leaking. Good luck.

  6. #19
    Join Date
    Jan 2008
    Location
    windy city
    Posts
    4,401
    Quote Originally Posted by Randy S. View Post
    If the unit has a rupture disk, I wouldn't go above 5 psi.
    i put in a pancake...........

  7. #20
    Join Date
    Dec 2007
    Location
    Central California
    Posts
    14
    I would check the sensor threads on the bottom of the purge. I have had to retap the threads. Also check the econimizer flange connection to the evap.

  8. #21
    Join Date
    Sep 2006
    Posts
    49
    Between the log readings, and the purge counts you will know if you have a leak issue. I have used the RefTec also, run 'till pressure gets to 7 psig using an accurate gauge. If you want to go above 10 psig you might want to fit up the back side of your pressure relief vent line, and install a line to keep the pressure equal on both sides of the disc. Isolating the condenser water valves at the barrel will usually prevent any problems getting the pressure up.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event