Results 1 to 13 of 16
    Nov 2009
    Northern Alberta
    Furnace combustion air
    I'm installing a 70000 BTU furnace into a confined room below a house. The room is approximately 8 feet square by about 7 feet high, so I'll need to bring in combustion air from outside. I did the calculation, and should require 2 vents, one for intake within 12" of the floor and one for exhaust within 12" of the ceiling. According to my calculation, they should be a minimum of 35 sq in surface area each. The closest round pipe size is 8" which is about 50 sq in. I mentioned this to another pro and he figures its way too much and if it's -40C outside or colder, the furnace won't be able to heat the home efficiently. He figures a 5" pipe for each is good enough, but this of course would not satisfy the code requirements. We live in northern Alberta where it can get very very cold! Any thoughts on how to alleviate this?
    Nov 2008
    How much combustion CFM you need, at how many inches of water?
    Tn.
    yea get somebody that knows about it to install it.
    not guessing at things
    Nov 2009
    Northern Alberta
    Furnace is a Lennox (mid efficient G40UH(X)). I don't see the CFM's listed for it, but they specify in the manual to have 2 air openings free area of at least one sq inch per 2000 BTU per hour of the total input rating (of all equipment in the enclosure). It has an input rating of 70000 BTU thus the calculation of 35 sq inches per vent.
    The home is at about 2000 feet elevation.
    S.E. Pa
    Cool top end heated power MUA
    http://www.sheltersupply.com/corpora...t.asp?cwpID=16
    You could use a Hoyme damper made right in Alberta but it does not have the duct heater.
    HTH,
    Hearthman
    Nov 2009
    Northern Alberta
    Does anyone know how significant the impact is of bringing in extremely cold combustion air to the efficiency of the system? Would perhaps installing a longer intake pipe inside the crawl space help?
    Nov 2009
    Northern Alberta
    Thanks Hearthman, I will look in to that.
    Nov 2009
    Northern Alberta
    I found out that I can get 7" insulated flex duct and all I need for residential (here in Alberta) is one vent for the supply (from the outside) and must terminate within 2 feet of the burners and within 12" of the floor. The cold air shouldn't impact the efficiency too much.
    Aug 2009
    Beatrice, NE
    If a proper load had been done on the house the combustion air would have been figured into the furnace size so having the right size pipe should not be a problem for the furnace to over come the extra cold air needed.
    Nov 2009
    Northern Alberta
    In this application, none of the combustion air is coming from inside the house. The floor is sealed with vapour barrier and is insulated. The crawl space currently is unheated, but eventually an insulated foundation will be installed and can then be heated if desired. There currently will be some leakage of air from the crawl space into the furnace room. The crawl space is partially insulated but not airtight to the outside as well. This will change as this mobile home will be put on a full foundation and function more like a house.
    just a question/suggestion
    why not use a 2 pipe system, intake and exhaust from outside in PVC/ABS/DWV (code compliant)?
    Jul 2005
    Stokes; One way to solve the problem is to bring in a single pipe of adequate ( 5", 6", or 7") diameter and terminate it at the furnace room FLOOR level using 2-90 degree elbows so that they form the letter "U".
    This will make an "air trap" and will provide air for combustion ONLY IF NEEDED.
    Without this "U" formation unwanted (cold) air would come into the area even when it's not required. (it's known as the "anti-spill" method) make sure you install a SCREEN onto the outside intake to avoid any entry of insects, etc.
    try it , I think you will like it.
    Nov 2009
    Northern Alberta
    That sounds like a great idea. Thanks for that deejoe!