Thread: reach-in lite problem
-
11-18-2009, 07:36 PM #1
Professional Member
- Join Date
- Dec 2006
- Location
- philadelphia pa
- Posts
- 159
reach-in lite problem
This may be a stupid question but, working on a reach-in today, no lites so I replaced the bulbs, still no lite. So I replaced the ballasts, still no lite. PLEASE LET THERE BE LITE!! Is there any way to check the ballasts and or tubes? 120 volts present at the ballast. I tried to check voltage at the socket, top and bottom =0 volts any ideas?
-
11-18-2009, 07:40 PM #2
are the door switch contacts working properly?
-
11-18-2009, 07:44 PM #3
Professional Member
- Join Date
- Nov 2008
- Location
- S.C.
- Posts
- 914
I'm wondering if there is anything else in the circuit. Like a little miniature aluminum can looking gadget? I think its a starter if I remember correctly. (or something like that)
It's refreshing to pull your head out of the box when servicing a system.
-
11-18-2009, 08:05 PM #4
-
11-18-2009, 08:13 PM #5
Some units have a thermostat running the lights
If You Can Dodge A Wrench You Can Dodge A Ball
-
11-18-2009, 09:16 PM #6
Professional Member
- Join Date
- Dec 2006
- Location
- philadelphia pa
- Posts
- 159
I didn't see a door switch
4 door reach-in, the lites on the left side are working
on the ballast, should I be able to read potential at the leads? 4leads for each lite
-
11-18-2009, 09:46 PM #7
I've had bad connections/loose wires at the bulb sockets before that will drive ya nutz like this.
If You Can Dodge A Wrench You Can Dodge A Ball
-
11-18-2009, 09:51 PM #8
You have to also watch the bulb output HO or VHO ???? One works in the cold and one doesn't.
And what the others said about the starter. Unless they are electronic. Somedays you need 20 new starters find one good one. Watch for new duds in the starter area.
-
11-18-2009, 09:59 PM #9
Regular Guest
- Join Date
- Nov 2008
- Posts
- 1,656
The only thing left besides the starters are the lamp sockets, the "tombstones."
Also make sure the index mark on the tube ends shows that the tube is fully rotated into the socket correctly.
On tubes with two pins on the end, there should be a few volts across the pins to heat the filament.
Also, some lamps don't start reliably unless the metal Ground Plane (the metal case) near the tube is grounded.
-
11-18-2009, 11:32 PM #10
Some reachins have the door switches in the door hinge.
-
11-19-2009, 05:03 PM #11
I checked today. You still can buy a *wand* from any bulb supply house to check output.
I have one, but haven't used it for decades. I got snagged up on VO and HVO BULBS once and it drove me nuts. The wand didn't help with that VHO issue.
-
11-19-2009, 05:15 PM #12
Regular Guest
- Join Date
- Nov 2008
- Posts
- 1,656
-
11-19-2009, 05:33 PM #13