    Carrier 19XR loading fault

    Anyone had any problems with a Carrier 19XR. This one refuses to load fully past 75-80% or so because of an approach temperature problem. All I can think is either refrigerant charge, flow rates incorrect, fouled tubes, faulty sensor.

    I was just thinking that someone may have a different take on it....

    Thanks
    A problem shared is a problem halved

  2. #2
    Join Date
    Jun 2008
    Location
    Windsor, Ont.
    Posts
    458
    Assuming you have the IOM this is what Carrier says to check.
    Some operational data readings would also be helpful.

    162 SENSOR ALERT EVAPORATOR
    APPROACH
    162→Evaporator Approach
    [VALUE] Exceeded Limit of
    [LIMIT]*.
    Check that refrigerant charge level is adequate,
    waterbox division plate gaskets are sealing,
    evaporator tubes are not fouled and that oil
    reclaim system is working.
    Check sensor resistance or voltage drop.
    Check for proper wiring.
    Check Evap Approach Alert setting in SETUP1
    screen.
    163 SENSOR ALERT CONDENSER APPROACH 163→Condenser Approach
    [VALUE] Exceeded Limit of
    [LIMIT]*.
    Check sensors resistance or voltage drop.
    Check for proper wiring.
    Check Cond Approach Alert setting in SETUP1
    screen.
    Check for noncondensable gas in the
    condenser.
    Check that the condenser tubes are not fouled.

  3. #3
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,609
    The obvious first question is "What's your approach temp?"

  4. #4
    Join Date
    May 2004
    Location
    Under The Milky Way
    Posts
    129
    Actually it had been manually limited to 80% by someone else.

    I noticed the oil level was just to the bottom of the second sight glass. No flashing in the motor cooling line sight glass. Refrigerant temp 2.7 degrees leaving water was 8.9 degrees so 6.2 degrees approach (sorry these are celcius) approach alert 162 triggers at 2.8 degrees C.

    After running for a while at 95% approach was slightly decreasing so perhaps some oil logging in the cooler ??
    A problem shared is a problem halved

  5. #5
    Join Date
    Dec 2006
    Location
    Richmond Va
    Posts
    2
    I just placed two brand new 19XR"s into service and I am receiving alarms on one of them. I too have seen in the alarm history warnings of approach problems. I have placed a service call too Carrier about this since it's under warranty by the contractor. I will let you know what they find.

  6. #6
    Join Date
    Mar 2008
    Location
    philadelphia
    Posts
    312
    approach is high, do you have oil issues or have you had to add oil, need a full set of readings to really tell you more load pressures , drops etc... water and refrigerant side plus deesign if you have it.

  7. #7
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,086
    In I-P terms you are speaking about an 11 degree approach on the evap side.

    Regardless, when someone says "I can't get a chiller to load past such and such %", the follow up sentence I want to read is "and the chiller isn't meeting the load" but for some reason that follow-up wording is often missing. If the chiller meets the load at all times but never loads past, say, 80%, could it mean the chiller is a bit oversized for its given "full load" condition?

    Or are you speaking about not being able to manually open the guide vanes to get the chiller amps to go past, say, 80%? Are we speaking about % of vane opening or % of full load amps?

    The more precise information you give, the more precise answers you will receive.
    • Electricity makes refrigeration happen.
    • Refrigeration makes the HVAC psychrometric process happen.
    • HVAC pyschrometrics is what makes indoor human comfort happen...IF the ducts AND the building envelope cooperate.


    A building is NOT beautiful unless it is also comfortable.

  8. #8
    Join Date
    May 2001
    Location
    Western Wa
    Posts
    1,758
    Got leaks?
    God Bless the USA

  9. #9
    Join Date
    May 2004
    Location
    Under The Milky Way
    Posts
    129
    high cooler approach which at near full load is around 8-10 degrees F (5-6 degrees C) the oil level looks low in the compressor as well. The skimmer line sight glass was clear. At part load 60% amps and 30% guide vanes the appraoch is much lower (1.3 degrees C or 2.5 degrees F) there is liquid flashing in the skimmer line sight glass and the alert is gone. I checked the resistance of the thermistors which seem OK. The flows are near enough, only marginally low. My deduction is that there is a refrigerant shortage, as at fuller load the liquid in the cooler is below the skimmer line, which leads to poor oil return (the level is lower). Another identical chiller runs mormal oil levels, and a 0.2 degree C approach, with flashing in the skimmer line.

    I couldn't pick up any obvious leaks, but that doesn't mean they aren't there. It's a reasonably new machine 3 or so years old. I screen printed all the figures from my service tool but they are on my other computer..
    A problem shared is a problem halved

  10. #10
    Join Date
    May 2001
    Location
    Western Wa
    Posts
    1,758
    Try playing with the condenser temp before you give up and take it apart.
    Maybe you don't have enough bubbles to float the float.


    Another idea might be to go around the float with a hose and some fittings to try to figure out what's going on.
    God Bless the USA

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event