Results 1 to 7 of 7
Thread: dark green sludge
11-13-2009, 10:39 PM #1
- Oct 2009
- ma
- 40
dark green sludge
we changed a condenser during the summer, evap on first floor , condenser on roof of 5 story building, before changing condenser( which boss condemned) he wanted me to isolate piping from evap to pressurize to make sure no leaks. i found oil acidic didnt need tester felt on hands and smelled it. well lines were tight so reconnected swapped out condenser installed 2 core sld and used burnout cores, month later changed cores ll drier cleaned out shell from green sediments, month later changed again, but removed shell piped in unit changed ll drier again, even though oil was clear and had no oder is this condenser still at high risk of damage or should it be fine
just wondering what people think
11-13-2009, 10:50 PM #2
- Sep 2005
- Texas
- 2,793
do the acid test...it's trust worthy
11-14-2009, 07:44 AM #3
Green slime. Water got into the oil in the old system. Change the refrigerant lines, indoor coil and outdoor unit at the same time. It is like cancer, leave a little in and it will come back.
If you just changed the condensor, then you have an oops. Another good reason to sell only matched systems.Remember, Air Conditioning begins with AIR.
11-14-2009, 09:53 AM #4
Banned
- Dec 2006
- Middle Tennessee
- 11,347
11-14-2009, 10:38 AM #5
Probably not the dreaded green slime, but more a cousin of it. Unless this was one of the early versions of the Copeland scroll compressor, it is most likely a similar condition that happens with yellow compressor oil. Green slime only forms in the white mineral oil that copeland used on their scroll compressors.
The darker sludge that occurs is heavier and does not go throughout the system like green slime does. It can usually be cleaned up, but is still some messy stuff.Government is a disease......masquerading as its own cureEcclesiastes 10:2 NIV
11-14-2009, 11:55 AM #6
Banned
- Dec 2006
- Middle Tennessee
- 11,347
11-14-2009, 08:42 PM #7
- Oct 2009
- ma
- 40
i didnt agree with changing only condenser, bosses decision, everything i did my boss told me to do, i said it may be problematic. he said after two filter changes it was fine, he didnt want to pay for the acid test to be sure. i know it was a bad one , i could feel it irritating my skin, and damn near lost all my nose hairs from smell.
well like said i am just kind of waiting for problem, i questioned it when he did it but what do i know.