Results 1 to 13 of 34
    Nov 2009
    RTAA 1254 trane chiller
    unit is going off on "oil flow control" both compressors. unit does not have oil flow control or oil pressure switch. it is monitored by temp. thermistors. This diagnostic code is not in the book. Does anyone know what this is?
    ottawa canada
    You will never guess..... you have low oil flow ?????
    in a tree looking in your window
    Something doesnt add up here Dave, you say you have a RTAA125 and you are correct they have temp sensors that verify proper oil flow, on RTAAs from 130 tons and up they have a oil differential pressure switch that the micro "tests" every time it stops a compressor, if the oil switch doesnt pass the test it alarms out with "oil flow control".
    Your RTAA 125 should alarm with oil system fault, are you sure of what machine you have here. If it is a RTAA125 or smaller it will have a clear language display where you actually read the alarm messages, if it is a RTAA130 and up it will have a blue LED screen that will give you a diagnostic code that you have to cross over on a chart.
    Which book do you have? RTAA125 and smaller is RTAA-IOM4A and the RTAA130 and up is RTAA-IOM-3 at least thats what they used to be.
    If you dont stand behind our troops, please feel free...........to stand in front of them.
    Jun 2009
    Florida
    Quote Originally Posted by Dave_87 View Post
    Yes it is. Take another look at page 96. Assuming you're looking at the right book to begin with.
    Low Pressure Forever!
    If you know heavy metal, you can work anywhere-Dave Andreson
    Anchors Aweigh my boys, Anchors Aweigh!
    Farewell to foreign shores, We sail at break of day. Through our last night on shore, Drink to the foam. Until we meet once more. Here's wishing you a happy voyage home!
    Apr 2009
    In the south
    Oil temp is falling more the 4 degrees below sat cond. temp. Check all sensor for correct readings and check to ground. If there is any reading to ground you should change the sensor. You are more they likely slugging ref. back and cooling the oil. It is usually a bad sensor.
    Nov 2009
    Yes. I have a RTAA 1254 and looking at book RTAA-IOM-4A and the clear language display reads "oil flow control cprsr A". Its not reading "Low oil flow" or "oil system fault". The unit will run about 5 to 10 minutes somtimes or it will run 2 hours then shut down on this code.
    Nov 2009
    if it was a sensor problem would it have to run for 30 minutes before shutting down on " oil system fault"
    Nov 2009
    the clear language display shows " oil flow control" not " oil system fault" like on page 96
    ottawa canada
    Dirty coils
    N.E. IA
    Check you configuration. Sounds like you have the wrong compressors configured.
    I had one like that a while ago. Everyone kept thinking it was an "Oil Flow" problem where the wording is actually "Oil System Fault" .
    Found the controls were configured for the wrong compressors.
    "Wheel" mechanics work on "Wheel" chillers
    Nov 2009
    I cleaned the coils thursday
    N.E. IA
    Sorry, Grabbed the wrong quote. I meant "Oil Flow Control" fault, like you said.
    ottawa canada
    Do all the fans run and are they going the right direction ?? you say you cleaned the coils , the oil cooler is in the top passes of the coil are they REALLY clean ???