Results 1 to 7 of 7
Thread: ASHRAE help!!!
-
11-13-2009, 10:11 AM #1
Regular Guest
- Join Date
- Aug 2009
- Posts
- 33
ASHRAE help!!!
i am trying to purchase 85% efficiency filters for my AHUs at work. But the sales people from filters are keep giving me ASHRAE standard 52.1 certificate which says that MERV-13 are 85%, but according to ASHRAE 52.2 they are <75%. Is ASHRAE 52.1 still accepted by FDA etc?
Thanx
-
11-13-2009, 11:33 AM #2
Professional Member
- Join Date
- Sep 2006
- Posts
- 685
z
The 80-85% efficiency filter you are seeking is generally accepted as a MERV 13. The problem is the numbers are derived by totally different test methods. The 75% you are seeing in the 52.2 test is a percentage of particle capture by particle size. The 80-85% in the 52.1 test is a "dust spot efficiency" which is the discoloration of a "target" exposed to test dust on the downstream side of the filter.
The 52.1 standard has been "retired" which means it won't be accepted by the FDA.
For a review of the current ASHRAE filter testing situation see:
http://allergyclean.com/articles/?p=157
-
11-13-2009, 11:54 AM #3
Regular Guest
- Join Date
- Aug 2009
- Posts
- 33
-
11-13-2009, 11:58 AM #4
Professional Member
- Join Date
- Sep 2006
- Posts
- 685
You can use a MERV 13.
-
11-13-2009, 12:01 PM #5
Regular Guest
- Join Date
- Aug 2009
- Posts
- 33
-
11-13-2009, 12:55 PM #6
Professional Member
- Join Date
- Sep 2006
- Posts
- 685
z
You need to read the article.
An 80-85% filter tested according to 52.1 has nothing to do with efficiency at 0.3 microns. If for some reason you actually need 85% efficiency at 0.3 microns, the only filter that will provide this is a true HEPA. The 85% you are reading off the ASHRAE 52.2 chart is actually an average for 4 particle sizes between 0.3 and 1 micron. A MERV 14 filter would generally provide less than 70% efficiency at 0.3 microns.
-
11-20-2009, 07:20 PM #7
Regular Guest
- Join Date
- Sep 2009
- Posts
- 17
Add a rack for carbon filters!!!


Reply With Quote