    noisy cold air return

    I have a goodman AEPT 060 5 ton variable speed air handler and heat pump heating and cooling my 4000 sq ft home in washington state. I had a 16" cold air return in central part of home and a seperate 10" return in master bedroom but noticed a lot of noise coming from my 16" cold air return. I decided to add an additional 12" return about 15' away from the existing 16" return in hopes this would quiet the system down. Now the noise is coming from the 12" return(whistling noise). The 12" return is basically a 12"x12" box that transitions to 12" round pipe. From the back of that is 25' of insulated flex duct going into my cold air return box on top of my air handler. Any ideas??

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,766
    Your installer didn't size the returns right.
    call him back, and have him redo them the proper way.


    PS: Don't make duplicate threads about the same problem. I deleted your other thread.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    Nov 2009
    Posts
    5
    ok, i don't think I can blame hvac guys this time. They had originally installed a seperate additional 16" supply and return in a racquetball court in my home but since it seemed to be cold in there and since wasn't being used much I capped off supply and returns to this room myself. Are you saying that with a 16" return a 12" return and a 10" return that I still don't have sufficient return air?

  4. #4
    Join Date
    Nov 2009
    Posts
    5
    I calculated out available sq. in of cold air return to be 391 sq. in.

  5. #5
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,766
    Sorry, this is not a DIY site. So we are not allowed to give out DIY advise.

    Please read Site Rules Thank you.



    But, I wasn't taking about your ducts.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  6. #6
    Join Date
    Oct 2006
    Location
    The Beach
    Posts
    747
    You don't need to blame the HVAC contractor, just ask him to fix it.
    Blue Fox

  7. #7
    Join Date
    Nov 2009
    Posts
    5

    problem solved

    I took off the new 12x12 cold air return grille and noise went away. I was looking for a bar style grille that has better airflow when I decided to just try and bend the vent slats on existing grille. The noise(whistling) is gone completely and the system is quiet again. Not sure if the 410 cu. inches of return air is enough for 5 ton system or not. I did reduce the fan c.f.m to 1600 cfm down from 2000. Seems to be working great.

  8. #8
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,766
    1600 CFM in heating mode. That will tend to shorten compressor life span.
    And lower the heat pumps efficiency.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  9. #9
    Join Date
    Nov 2009
    Posts
    5

    cfm

    Sorry, I lied. It was lowered to 1835 rpms . Does that sound better or is there a reason to leave it on highest setting which is 2050 rpms?

  10. #10
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,766
    The 1835 is ok.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event