Good day Sysint,
Indeed, in regards to my comment about the Neuron chip's possible future issue(s) the risk is small, but nevertheless there. Where this differs from BACNet (assuming one implements their own BACNet stack) is that if there is a protocol issue (i.e. bug) a manufacturer has the ability to sort it out...as the the problem can be corrected in firmware (assuming the problem is not a faulty hardware design). Using a Neuron chip (or a dedicated third-party BACNet chip), the manufacturer is hooped and at the mercy of the Neuron (or BACnet) chip manufacturer to fix the problem. Secondly, if it is shown that the chip itself has issues, then the only solution is to replace the chip... which is not very simple or economical
Now, to be fair there are other single sourced chips in the manufacturer's design... such as the microcontroller or microprocessor, however, because these chips are generic they are sold in much higher volumes (100's of thousands, millions, etc) and so major bugs within them would have been resolved fairly early on in their release.
I make these points as items to be aware of and not meaning to slight any one vendor or protocol.
Cheers,
Sam
-
11-11-2009, 12:47 PM #16
Permanently Removed
- Join Date
- May 2002
- Posts
- 9,564
Well yes I suppose. However, you can implement LON off the chip. - Anyway, it's not like there is one way to do this. However, this one is rather inexpensive.
-
01-21-2010, 11:53 AM #17
New Guest
- Join Date
- Jan 2010
- Posts
- 3
The full-load (32 device) transceivers are more noise-immune than the 1/4 or 1/8 load RS485 transceivers. VFD's often use the full-load transceivers, because of this. A 480VAC VFD has about 600VDC on their power circuitry which is physically located close to the isolated RS485 circuits. In many cases it is not about saving a few pennies, it is often about the quality of communications.
-
01-21-2010, 12:49 PM #18
Professional Member
- Join Date
- Feb 2005
- Location
- Edmonton, AB Canada
- Posts
- 509
Good day AbeS187,
I do not know if you can say this across the board for all 1 Unit Load (UL)RS-485 transceivers. By definition a RS-485 transceiver must comply with the minimum requirements which are set out in the electrical specification(s) for the RS-485 (or should I say EIA-485) devices. Some manufacturers exceed these minimums and some offer devices which guarantee these "enhanced" specifications... but not all. Remember if the specs are not "guaranteed" then you cannot assume that these enhanced specs will always be available as these specs can and will change on the respective manufacturing run. For specific design critical specs I always qualify a manufacturer and I will not allow a alternative manufacturer's component substitution unless I have qualified this new vendor's part. Sadly, at times purchasing department personnel see all components as generic and as such feel they can interchange parts (assuming functional/footprint compatibility, etc) based upon pricing... this is indeed not so on a number of components that are deemed critical to a circuit's functionality and reliability.
Another item which may be related to your comment is that the 1 UL devices have a lower input impedance (minimum of 12K ohms by spec) than the 1/4 UL (48K ohms) or 1/8 UL (96K ohms) devices which in itself may offer less susceptibility to noise.
Cheers,
Sam
-
01-21-2010, 02:43 PM #19
New Guest
- Join Date
- Jan 2010
- Posts
- 3
-
01-21-2010, 03:09 PM #20
Professional Member
- Join Date
- Nov 2006
- Location
- New Hampshire
- Posts
- 255
MORE immune to noise. less susceptibility to noise.
Aren't these two statements the same?
-
01-21-2010, 03:30 PM #21
New Guest
- Join Date
- Jan 2010
- Posts
- 3
-
01-21-2010, 03:59 PM #22
Professional Member
- Join Date
- Feb 2005
- Location
- Edmonton, AB Canada
- Posts
- 509
Good day Abes187,
The Input impedance by itself will not always guarantee higher immunity to noise. Remember that RS-485 is a differential signalling medium and as such common-mode noise will be cancel out... i.e. the same noise (assume common-mode) will be present on both terminals independent upon the input impedance and therefore will be canceled out... This is assuming, of course, that cabling is correct for RS-485 (suitable twisted pair, daisy chaining, etc).
Cheers,