  1. #1
    Join Date
    Mar 2005
    Posts
    664

    carrier 30gh flotronic 1990

    Hello gents
    ,hope all is well. I need to know firstly is it possible to convert old carrier 30gh flotronic to txv? and if so how to go about it. the 30gt has a setpoint for txv or exv , the 30gh doesnt appear to . I read somewhere about a kit for retro, eprom required? Site wants to convert to 407c/poe, 1990 chiller, I guess im also wondering if its possible to install txv and lls and ignore exv modules? or would that bring up alarms not seeing the windings? other option upgrade exv and drivers? that maybe quite pricey, thanks for input! stan
    Keep it simple to keep it cool!

  2. #2
    Join Date
    Mar 2005
    Posts
    664
    looking through alarm list it looks like failure to pump down will also be an issue, not sure where that signal could be picked up from...
    Keep it simple to keep it cool!

  3. #3
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,710
    What type of control panel does this chiller have? How about a model number?
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  4. #4
    Join Date
    Mar 2005
    Posts
    664
    hi Dallas carrier 30gh-260-0017ee , flotronicII , HSIO keypad circa 1990

    stan
    Keep it simple to keep it cool!

  5. #5
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,710
    Is that with the PSIO module?

    Quote Originally Posted by stanbyyourword View Post
    hi Dallas carrier 30gh-260-0017ee , flotronicII , HSIO keypad circa 1990

    stan
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  6. #6
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,710
    http://www.docs.hvacpartners.com/idc...1-30011-25.pdf

    Here is the USA answer to refrigerant conversion.
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  7. #7
    Join Date
    Mar 2005
    Posts
    664
    yes PSIO processor and HSIO keypad http://www.youtube.com/watch?v=SZDZPeJ1fNo exact same chiller , except my keypad is all black with white buttons stan
    Keep it simple to keep it cool!

  8. #8
    Join Date
    Mar 2005
    Posts
    664
    Going with r407c vs mo99 with existing exv , and poe oil change , wish me luck stan
    Keep it simple to keep it cool!

  9. #9
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,710
    I would think you will be ok I early on they made our 30GTN's in R-22 and the alternative at the time was R-134a but that was a few years ago.

    I have not seen a 407c conversion here as of yet.

    Good Luck let us know how it goes.


    Quote Originally Posted by stanbyyourword View Post
    Going with r407c vs mo99 with existing exv , and poe oil change , wish me luck stan

  10. #10
    Join Date
    Mar 2005
    Posts
    664
    ok I will, pt relationship is close enough , if only they had parameters lik 30gt and 30gb option of exv/txv I would put 407c txvs in w LLsolenoids.
    fingers crossed , less than 2 years life left for this chiller stan
    Keep it simple to keep it cool!

  11. #11
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,710
    Agreed
    Quote Originally Posted by stanbyyourword View Post
    ok I will, pt relationship is close enough , if only they had parameters lik 30gt and 30gb option of exv/txv I would put 407c txvs in w LLsolenoids.
    fingers crossed , less than 2 years life left for this chiller stan

  12. #12
    Join Date
    Apr 2007
    Location
    uk
    Posts
    184
    You can change the refrigerant setting in the factory and service configuration to R407C from R22

  13. #13
    Join Date
    Apr 2007
    Location
    uk
    Posts
    184
    You can change the refrigerant used in the factory and service configuration codes from R22 to R407C

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event