    Im curious how many people are doing tower optimal control, and for those that are what strategies are you using?
    Go Rangers!
    We do this alot. We control tower fan speed to maintain a calculated CWFT setpoint. CWFT setpoint is calculated based upon outside air wetbulb + an approach temperature of something like four degrees. Need to set limits on the setpoint based upon chiller information, a common low end is 65 degrees.
    Jan 2002
    Thanks for the info Travis.
    Go Rangers!
    Pacific Time Zone
    Doing a similar thing - only when you have everything with Econo-coils you can run the loop a lot cooler.
    BTW - Is CWFT - Condenser Water Fan Temperature Setpoint?
    San Diego, CA
    Quote Originally Posted by crab master View Post
    Maybe Condenser Water From Tower? as opposed to CWTT
    SoCal
    We like to control tower fan speed from head pressure inputs to a PI control loop. We have a building that includes a 300 ton evap condenser with 2 separate DX refrigeration circuits. Pressure transducers installed on the liquid line are wired to a couple Circon GPC controllers which send the values to an iLON which selects the highest signal and transmits back to the Circon controller. The GPC controller uses a PI function and sends the speed signal to a Yaskawa VFD that has a LON card installed. It works really well and holds head pressure on mild days within +/-5 PSI of setpoint.
    Recently we added a flow meter on the makeup water line and added the makeup water flow gpm to the network. We log the data every 15 minutes and were amazed when there were a few days this summer where the tower consumed close to 5,000 gallons of water a day! We can also detect if the float valve leaks during shut-down hours. Next phase will be to add TDS and PH sensors.
    Cheers,
    lb
    A hundred million nodes - it's a LON story.
    Oct 2009
    Optimization?
    Quote Originally Posted by tshort View Post
    That's not really optimization though, is it? More of a strategy, but it doesn't really optimize the system.
    Trane has a strategy, and I could tell you what it is, but then I'd have to kill you.
    Oct 2009
    Quote Originally Posted by lonboy View Post
    Cheers,
    lb
    Quick question - is this being done on a chilled water plant with centrifugal compressors? I think that you would end up with a lot of surging.
    SoCal
    Quote Originally Posted by SubCoolWasTaken View Post
    No, this is a DX plant with (2) Carrier 5H120's. On another job we did similar head pressure control of tower fans with a Carrier Screw 30GT chiller running R134A equipped with LON translator card. Discharge pressure from the chiller was sent onto the network and a freely programmable LON device did the rest.
    At the end of the day, it's the head pressure that counts! Not too high and not too low!