    cracked heat exchangers

    i took a heat exchanger class the guy said to pull the blower and spray the heat exchanger with high concentrated dish soap then pull the burners to check if any soap went thru. i tryed it a few times but never found a crack he also said a tracer gas will work. does anyone have any good tips

  2. #2
    Join Date
    Jun 2000
    Location
    B.C. Canada
    Posts
    147
    Post Likes
    Is that a serious suggestion? Inspection with a scope or mirror, Smoke test, I have also closed all supply registers and watched the flame change. Lots of ways to check best is to remove the blower take a light shine it on the outside of heat exchanger and look for light through the burner inlets. This works on open clam shell style type found in older furnaces. RTU units just pull the top off or open up the inspection panel they are a lot easier than furnaces. Goodman I would remove the limit and slide my scope in you could see the rings cracking off or cracks in the exchanger, if it's really tough then you pull it out but only if your sure and you have to check it. I could go on and on with ways to check different furnaces you just figure out what works best for you.

  3. #3
    Join Date
    Sep 2009
    Location
    Stumptown,USA
    Posts
    1,257
    Post Likes
    Juluous just about covered it. A carbon monoxide detector really helps too. Go to www.tpi-thevalueleader.com and look at the HXG-2 and HETKIT this is the tracer gas method you mentioned in your post.

  4. #4
    Join Date
    Sep 2002
    Location
    I don't know
    Posts
    3,047
    Post Likes
    A carbon monoxide detector really helps too.
    How?

    The combustion side of induced draft furnaces operates under a slight vacuum.

    I doubt that a co meter can detect bad heat exchangers, unless there's a crack which allows the air stream to blow combustion byproducts out the inlets. (where the burners are)

  5. #5
    Join Date
    Sep 2009
    Location
    Stumptown,USA
    Posts
    1,257
    Post Likes
    There are still a lot of natural draft furnaces out there. Also you can check the flue gasses on a gaspack to see if the flame is burning clean. Maybe thats why the guy giving the class suggested the soap trick and tracer gas test kit.

  6. #6
    Join Date
    Apr 2001
    Location
    Western PA
    Posts
    1,811
    Post Likes
    Quote Originally Posted by vapor hvac/r View Post
    i took a heat exchanger class the guy said to pull the blower and spray the heat exchanger with high concentrated dish soap then pull the burners to check if any soap went thru. :
    Not concentrated soap, I use water with a few drops of soap. It works, just need to practice. I sell a lot this way. The water washes the soot and rust out of the cracks and leaves a dark wet spot.
    Jason

  7. #7
    Join Date
    Apr 2008
    Location
    Pluto
    Posts
    984
    Post Likes
    A good combustion analyzer will help determine if a heat exchanger is bad. Have found quite a few that way.
    Not as lean, not as mean, but I'm still a hardcore, ass-kicking, hard charging Marine! Oohrah!

  8. #8
    Join Date
    Feb 2001
    Posts
    35,834
    Post Likes
    Their all cracked anyways, why bother.
    Hey cockroach, don't bug me! ©

  9. #9
    Join Date
    May 2004
    Location
    Toronto
    Posts
    276
    Post Likes
    water is the best soak down the outside of the heat exchanger and look for wet spots inside

  10. #10
    Join Date
    May 2009
    Location
    Paragould, AR
    Posts
    113
    Post Likes
    At Comfortech 2009 this year, there was a small company selling this UV dye and flightlight kit for checking HX. You took a screw out somewhere, and with a long metal tube, sprayed the dye all over the outside of the HX. Then you took the UV light and looked inside it, or vice versa. Anybody tried something like this in the real world? It looked impressive, but I had my doubts on the tube type HX's.

  11. #11
    Join Date
    May 2004
    Location
    Toronto
    Posts
    276
    Post Likes
    i have been doing this for 15 years and water has never failed and it is free

  12. #12
    Join Date
    Oct 2009
    Posts
    30
    Post Likes
    Thread Starter
    the guys name is ellis from heat exchanger experts the book that comes free when you take the class tells you where to find the stress point in the heat exchanger for alot of differnt furnaces he sells a mirror that is long and comes with a pvc case to keep the glass safe. the class is alot of money but the company paid for it also his class his hard to take cuz you got to wait untill he comes to your city im from chicago and we had to wait to take the class.

  13. #13
    Join Date
    Mar 2008
    Location
    wi
    Posts
    282
    Post Likes
    I primarily do rtus my way is a well charged battery and cordless drill, I have carbon monoxide anyalizer but I don't trust it good or bad until I see it with my eyes. Yes I sound crazy but every rtu that I p.m I try to pull apart if easily possible, Yorks are easy, carriers, tranes. If its not easily possible then I used the anyalizer. Heck last week I had a really close buddy say that his co2 detector was goin off, I went over there did a co test then proceded to rip the oil furnace apart (resi). I don't like takin chances and jepordizing safety

  14. #14
    Join Date
    Mar 2008
    Location
    wi
    Posts
    282
    Post Likes
    I primarily do rtus my way is a well charged battery and cordless drill, I have carbon monoxide anyalizer but I don't trust a heat-x good or bad until I see it with my eyes. Yes I sound crazy but every rtu that I p.m I try to pull apart if easily possible, Yorks are easy, carriers, tranes. If its not easily possible then I use the anyalizer. But then even if I have a doubt I pull apart. Heck last week I had a really close buddy say that his co2 detector was goin off, I went over there did a co test then proceded to rip the oil furnace apart (resi). Everything was ok justa bad co detector the darn thing was goin off outside. I don't like takin chances and jepordizing safety

  15. #15
    Join Date
    Dec 2002
    Location
    Toledo, Ohio, United States
    Posts
    12,974
    Post Likes
    Twilli still uses Bon Jovi Twilli's pet hamster. Bon Jovi wears a little helmet cam and Twilli can sit on a stool and watch the monitor with the customer.
    No Heat No Cool You need Action Fast

  16. #16
    Join Date
    Mar 2003
    Location
    Cincinnati
    Posts
    7,977
    Post Likes
    Or you can see them clear as day without special tricks.








  17. #17
    Join Date
    Nov 2009
    Location
    Northwest GTA
    Posts
    4
    Post Likes
    if water is used, add a wetting agent which reduces waters surface tension to allow it to fall through a crack easier.

  18. #18
    Join Date
    Nov 2009
    Location
    Northwest GTA
    Posts
    4
    Post Likes
    for an extra step of security; if you use water, it would be a good idea to add a little amount of wetting agent to the water as it will reduce its surface tension and allow easier crack penetration quickly

  19. #19
    Join Date
    Jun 2009
    Posts
    147
    Post Likes
    what is the real deal with cracked heat exchangers?

    the blower makes positive pressure on the exterior of the hx the external pressure is greater then the internal hx pressure so flue gasses can not enter the the conditioned i.e. breathing air. except for the period of the fan delay.

    And the great prevalence of draft induced the hx is under further negative pressure - there are a few combustion blowers out there also gravity. If they have gravity it probably should be replaced for that reason alone or at least customer told that they should plan on it, unless they are 94yo with a furnace from 1952.

    So with draft induced and positive pressure on the hx what are in consequences of cracks revealed by extraordinary measures - beyond visual - flashlight works well.

    The way I see it, excluding a mound of rust, if visually it is ok and age is not an issue it is ok. A mound of rust a closer inspection or if there are problems.

    If the crack is enough to cause ignition problems that is serious. If the crack is enough that a enough flue gasses are entering the airstream yes. But a small opening found by removing the rust & soot (well there is another problem) and condeming the unit is to me questionable.

  20. #20
    Join Date
    Jan 2010
    Location
    In my van.
    Posts
    26
    Post Likes

    One good reason is............

    Quote Originally Posted by richvacr View Post
    what is the real deal with cracked heat exchangers?

    the blower makes positive pressure on the exterior of the hx the external pressure is greater then the internal hx pressure so flue gasses can not enter the the conditioned i.e. breathing air. except for the period of the fan delay.

    And the great prevalence of draft induced the hx is under further negative pressure - there are a few combustion blowers out there also gravity. If they have gravity it probably should be replaced for that reason alone or at least customer told that they should plan on it, unless they are 94yo with a furnace from 1952.

    So with draft induced and positive pressure on the hx what are in consequences of cracks revealed by extraordinary measures - beyond visual - flashlight works well.

    The way I see it, excluding a mound of rust, if visually it is ok and age is not an issue it is ok. A mound of rust a closer inspection or if there are problems.

    If the crack is enough to cause ignition problems that is serious. If the crack is enough that a enough flue gasses are entering the airstream yes. But a small opening found by removing the rust & soot (well there is another problem) and condeming the unit is to me questionable.
    MONEY! ITS ALL ABOUT THE CABBAGE

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •