Thread: busted belt gone wrong
-
10-24-2009, 08:13 AM #1
busted belt gone wrong
also tore up some control wiring in its path
To err is human, to really screw things up takes a service manager
-
10-24-2009, 09:48 PM #2
I've got a Lennox that did that. Took out the wiring to the condenser fan motors and wrapped them and the belt around the motor shaft. When it shorted it took out the fan relay, 1st stage compressor contactor and the control board. 460v on the control side isnt too good.
Zach
-
10-24-2009, 09:51 PM #3
Regular Member/Bad Email Address
- Join Date
- Jun 2000
- Location
- B.C. Canada
- Posts
- 147
I had a Lennox also do that, L-series unit flattened the discharge to the condensor.
-
10-25-2009, 09:00 AM #4
this was on a 50 ton carrier
To err is human, to really screw things up takes a service manager
-
10-25-2009, 03:35 PM #5
Regular Guest
- Join Date
- Apr 2006
- Posts
- 28
allso lookz lick the wrong size belt on that unit needs a bigger belt
-
11-07-2009, 10:02 AM #6
no that used yo be correct size... worn then snapped
To err is human, to really screw things up takes a service manager
-
11-07-2009, 01:28 PM #7
i've seen that happen on a new rooftop unit where the balancing guy had opened the motor pulley to the point the belt wedged in the pulley and then snapped. took out a lot of control wires. It looks to me like the motor pulley is opened up too far in this unit also, you might consider putting a smaller pulley on it
Steamfitters Local 602
-
11-08-2009, 08:22 AM #8
good observation, included in repair was a new sheave... yet adjusted much further closed
To err is human, to really screw things up takes a service manager
-
11-08-2009, 09:06 AM #9
If you close it up you are going to speed your fan up, you will get more air flow and a higher amp draw. I would put the new belt on it with the old pulley and amp the motor and then put a smaller pulley on it and adjust it until your amp draw is the same as it was with the original.
Steamfitters Local 602
-
11-08-2009, 09:15 AM #10
air/amp draw was low in the first place
To err is human, to really screw things up takes a service manager
-
11-08-2009, 09:53 AM #11
The adjustable sheave on this motor appears to exhibit little or no wear.
I find it best when working with adjustable fan drives to use a reflective tachometer, when speed comparison or adjustments become necessary.
The power of the motor changes the cube of the speed. A small variation in fan speed is a much larger change in power.
Just a hint from a regular member.
-