  1. #21
    Join Date
    Mar 2006
    Location
    Denver/Boulder
    Posts
    2,714
    Post Likes
    If the light isn't going on by now, I'm going to start worrying.

    What lies behind us and what lies before us are small matters compared to what lies within us.


    Two pressures, four temperatures = SUCCESS!


    Boulder Heating Contractor


    For Consumers:

    For HVACR Professionals:


  2. #22
    Join Date
    Mar 2006
    Location
    Denver/Boulder
    Posts
    2,714
    Post Likes
    Quote Originally Posted by acmanko View Post

    its called DX or Direct expansion.
    no, it's called DX or direct exchange.

    But, hey we all make mistakes.

    you're thinking of the other end of the system.

    Like I said, everybody thinks they already know what's out there.

    Mouth open, ears closed,

    instead of the other way around.
    What lies behind us and what lies before us are small matters compared to what lies within us.


    Two pressures, four temperatures = SUCCESS!


    Boulder Heating Contractor


    For Consumers:

    For HVACR Professionals:


  3. #23
    Join Date
    Aug 2001
    Location
    forney texas
    Posts
    21,087
    Post Likes
    Quote Originally Posted by darctangent View Post
    same answer.

    sorry, but you aren't listening.

    r-22

    r-407c

    r-410a
    I can't think of a loop that has refrigerant in it. refrigerant is in the AC system , the loop that makes it geothermal has water in it.

  4. #24
    Join Date
    Mar 2006
    Location
    Denver/Boulder
    Posts
    2,714
    Post Likes
    Quote Originally Posted by acmanko View Post
    I can't think of a loop that has refrigerant in it. refrigerant is in the AC system , the loop that makes it geothermal has water in it.
    What do you call the refrigerant cycle? Isn't that a loop with a pump in the middle?
    What lies behind us and what lies before us are small matters compared to what lies within us.


    Two pressures, four temperatures = SUCCESS!


    Boulder Heating Contractor


    For Consumers:

    For HVACR Professionals:


  5. #25
    Join Date
    Aug 2001
    Location
    forney texas
    Posts
    21,087
    Post Likes
    Quote Originally Posted by darctangent View Post
    What do you call the refrigerant cycle? Isn't that a loop with a pump in the middle?
    Yes, but that has nothing to do with a unit being geothermal. You can get heat from the air for a regular Heat Pump or heat from the ground with a Geothermal Heat Pump. Water is whats used in a geothermal system to transfer the heat from the ground via a pump and a tube in a tube condenser.

  6. #26
    Join Date
    Mar 2006
    Location
    Denver/Boulder
    Posts
    2,714
    Post Likes
    Quote Originally Posted by acmanko View Post
    Yes, but that has nothing to do with a unit being geothermal. You can get heat from the air for a regular Heat Pump or heat from the ground with a Geothermal Heat Pump. Water is whats used in a geothermal system to transfer the heat from the ground via a pump and a tube in a tube condenser.
    Oh lord.

    ok, envision this:

    you've got a conventional Heat Pump, but it's got a leak in the condenser coil.

    Oh, darnit, what to do?

    what to do, what to do?

    Whatever could we do?

    hmmm....

    How about this?

    we dig a trench in the ground and lay tubing in the trench, then we fill in the trench. we then connect the tubing to the condenser where it used to connect to the old condenser coil.

    now, the ground is the condenser. see?

    refrigerant travels through the "loop" or the "condenser coil" only now it's in the ground.

    no water.

    It's a little simplified, but that's how it all started.

    How is that NOT "geothermal" ?
    What lies behind us and what lies before us are small matters compared to what lies within us.


    Two pressures, four temperatures = SUCCESS!


    Boulder Heating Contractor


    For Consumers:

    For HVACR Professionals:


  7. #27
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    5,298
    Post Likes
    Instead of putting plastic in the ground and using water as an intermediate medium of heat transfer, you put copper in the ground and go direct. Hence direct exchange.

    Requires much less drilling, and a lot of refrigerant.

  8. #28
    Join Date
    Mar 2006
    Location
    Denver/Boulder
    Posts
    2,714
    Post Likes
    Quote Originally Posted by tedkidd View Post
    Instead of putting plastic in the ground and using water as an intermediate medium of heat transfer, you put copper in the ground and go direct. Hence direct exchange.

    Requires much less drilling, and a lot of refrigerant.
    yes, yes, and yes.
    What lies behind us and what lies before us are small matters compared to what lies within us.


    Two pressures, four temperatures = SUCCESS!


    Boulder Heating Contractor


    For Consumers:

    For HVACR Professionals:


  9. #29
    Join Date
    Aug 2001
    Location
    forney texas
    Posts
    21,087
    Post Likes
    Quote Originally Posted by darctangent View Post
    yes, yes, and yes.
    Ok, I see where you are coming from. Next question. Why not just break out the torch and repair the leak in the coil?

  10. #30
    Join Date
    Mar 2006
    Location
    Denver/Boulder
    Posts
    2,714
    Post Likes
    Quote Originally Posted by acmanko View Post
    Ok, I see where you are coming from. Next question. Why not just break out the torch and repair the leak in the coil?
    you are a tough crowd.
    What lies behind us and what lies before us are small matters compared to what lies within us.


    Two pressures, four temperatures = SUCCESS!


    Boulder Heating Contractor


    For Consumers:

    For HVACR Professionals:


  11. #31
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    5,298
    Post Likes
    :-)

    Bring a big recovery tank!

  12. #32
    Join Date
    Mar 2006
    Location
    Denver/Boulder
    Posts
    2,714
    Post Likes
    Quote Originally Posted by tedkidd View Post
    :-)

    Bring a big recovery tank!
    I'll take the cost of 2 jugs of refrigerant over the cost of drilling 3-5 times as much. I can also use better grout for better heat transfer.
    What lies behind us and what lies before us are small matters compared to what lies within us.


    Two pressures, four temperatures = SUCCESS!


    Boulder Heating Contractor


    For Consumers:

    For HVACR Professionals:


  13. #33
    Join Date
    Sep 2007
    Posts
    379
    Post Likes
    Quote Originally Posted by darctangent View Post
    I'll take the cost of 2 jugs of refrigerant over the cost of drilling 3-5 times as much. I can also use better grout for better heat transfer.
    Interesting. I have heard of this but have never seen a system. What size of copper line do you use and how many feet per ton? Say on a horizontal system. What are the cop"s? How do you work out your charge - based on length of pipe in the ground?

  14. #34
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    5,298
    Post Likes
    Quote Originally Posted by darctangent View Post
    I'll take the cost of 2 jugs of refrigerant over the cost of drilling 3-5 times as much. I can also use better grout for better heat transfer.
    Darctangent, are you being argumentative or trying to educate?

    If you are trying to educate it would be great if your posts had a bit more substance. For example, you could state that a direct exchange system uses 4lb + 4lb per ton, or a discussion about enhanced thermal grout/silica mixes and what you mean about your ability to use "better grout".

    Without that detail you might simply appear argumentative. That's my

    Quote Originally Posted by can2man View Post
    Interesting. I have heard of this but have never seen a system. What size of copper line do you use and how many feet per ton? Say on a horizontal system. What are the cop"s? How do you work out your charge - based on length of pipe in the ground?
    I believe you have 70 ft cores with 1-2 per ton. Not really set up for trenches yet, but they are experimenting with it in Tennessee, along with using the foundation perimeter on new homes. COP's are available at ahri I believe.

  15. #35
    Join Date
    Sep 2007
    Posts
    379
    Post Likes
    Quote Originally Posted by tedkidd View Post
    Darctangent, are you being argumentative or trying to educate?

    If you are trying to educate it would be great if your posts had a bit more substance. For example, you could state that a direct exchange system uses 4lb + 4lb per ton, or a discussion about enhanced thermal grout/silica mixes and what you mean about your ability to use "better grout".

    Without that detail you might simply appear argumentative. That's my



    I believe you have 70 ft cores with 1-2 per ton. Not really set up for trenches yet, but they are experimenting with it in Tennessee, along with using the foundation perimeter on new homes. COP's are available at ahri I believe.
    Thank you

  16. #36
    Join Date
    Mar 2006
    Location
    Denver/Boulder
    Posts
    2,714
    Post Likes
    I've got to get ready for an install tomorrow so this will be a little brief, but I'll try to cover some territory here.

    Quote Originally Posted by can2man View Post
    Interesting. I have heard of this but have never seen a system. What size of copper line do you use and how many feet per ton? Say on a horizontal system. What are the cop"s? How do you work out your charge - based on length of pipe in the ground?
    It depends on the application, but 3/8 & 1/2 or 5/8 are typical. When it comes to length, again system design will vary, but with vertical and diagonal bore holes you are talking about (1)100ft bore per ton with 100ft down, 100ft up so 200ft of tubing per ton, plus the copper to get back to the heat pump. I have never had a system that was designed for horizontal loops, but as I recall there are similar figures for that as well. COPs vary dependent on ground temp and soil conditions, but about 3 to 4.5. Nominal charge is about 7 lbs/ per ton on forced air with Domestic hot water, less on hydronic only systems. Charge is a little hard to explain, but very very easy to do. It relates to the metering system which is proprietary to Eathlinked. Suffice to say the metering system is like the old school refrigerators with a float arm in a reservoir of refrigerant. It sounds odd by modern thinking, but it's actually very efficient.- that's just part of it though- it's actually quite hard to explain in print only.
    Quote Originally Posted by tedkidd View Post
    Darctangent, are you being argumentative or trying to educate?

    If you are trying to educate it would be great if your posts had a bit more substance. For example, you could state that a direct exchange system uses 4lb + 4lb per ton, or a discussion about enhanced thermal grout/silica mixes and what you mean about your ability to use "better grout".

    Without that detail you might simply appear argumentative. That's my



    I believe you have 70 ft cores with 1-2 per ton. Not really set up for trenches yet, but they are experimenting with it in Tennessee, along with using the foundation perimeter on new homes. COP's are available at ahri I believe.
    Not trying to argue at all. If you read back to where this all started, I was simply pointing out that there is more to geothermal/ground source than water based systems. Then I got multiple responses essentially denying what I was saying. If there was an argument, it was about the requirement of using water in ground source systems. If you read back, I pointed out that I thought there were advantages and disadvantages to water source (as apposed to DX) Neither technology is perfect.

    On grout, bentonite based grout has a really nasty habit of stratifying in the bore hole causing the grout to fall away from the tubing and therefore poor thermal conductivity. My last two jobs I've used a cementitious grout called "supergrout"

    Another point- as I referenced earlier, horizontal loops do exist, and in some areas are the preferred method of install, but that in not the case in Colorado.

    All of this is dependant on the design laid out by the manufacturer, in this case Eathlinked.
    What lies behind us and what lies before us are small matters compared to what lies within us.


    Two pressures, four temperatures = SUCCESS!


    Boulder Heating Contractor


    For Consumers:

    For HVACR Professionals:


  17. #37
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    5,298
    Post Likes
    I'm no better at avoiding getting sucked in. Key is attempt to just give good information, particularly in response to ignorant and argumentative posts. Read Beenthere's stuff, he's usually really good at this (and some of the other guys).

    To some extent this is like kindergarten, everybody making noise wanting attention, but much is just noise without substance. People reading quickly sort through a lot of chaff to find good seeds. Only so much can stick (why fill the grey up with garbage, right?). The childish posts tend to blow away like deleting junk mail.

    Just thinking a lot of your stuff has seeds. Don't let others suck you into posting chaff.

  18. #38
    Join Date
    May 2007
    Location
    Michigan
    Posts
    529
    Post Likes

    IF YOU LIVE IN MICHIGAN-its not worth the trouble

    I worked for a company that sold waterfurnace and I think it was called international units. They got something back in arounds 1500 tax credit. The systems worked great once tuned in and would have a pay back of 100% in 11 years. But WOW the up front cost, did I say WOW, we did pond, horizontal earth closed loop, vertical well closed loop, and pump and dump.
    Here is what the fancy brochures leave out:

    Your yard / landscaping will need a complete overhaul once the heavy equipment is out, so if you can aford a GEO chances are you will at least have to replace about 10 - 15 grand in landscaping.
    Well drilling company - about 2000 a hole 4-6 in at 150 feet down.
    Dive team for pond loop - about 120 an hour.
    Heavy equipment rental is around 1600 a week for a loader and backhoe.
    Glycol - lots of the alien slime.
    A mile of sheet metal for your air handling units.
    Lots and lots of time for tuning.
    2 in diameter pipes punching through your basement wall (real fun to work with especially when they are cold).
    The actual water to air units weigh a lot so heavy some of the bigger members of your crew handy.
    Low end Geo for a small home was about 30-40,000 dollars at 2500-4000 ft squared and about 65-120,000 dollars at 5000-12000 ft squared homes

    Just wanted to let you know some of the un-glorious things about GEO, it is a great idea, but not in the north for small companies trying to profit. Just a headache, schools make it seem great (mine did), but unless you are out trying to sell people this stuff and trying to put it in then I would not waste my time with my nose in a book trying to memorize calculations and practicing design principals. You need to find a local that does it, volunteer to help on a system and get your own perspective, I know after getting out of the HVACR design program at school and actually doing it I was left with a sour taste.

    But IGSHPA is the source for all GEO.

  19. #39
    Join Date
    Mar 2006
    Location
    Denver/Boulder
    Posts
    2,714
    Post Likes
    Quote Originally Posted by durussel78 View Post
    I worked for a company that sold waterfurnace and I think it was called international units. They got something back in arounds 1500 tax credit. The systems worked great once tuned in and would have a pay back of 100% in 11 years. But WOW the up front cost, did I say WOW, we did pond, horizontal earth closed loop, vertical well closed loop, and pump and dump.
    Here is what the fancy brochures leave out:

    Your yard / landscaping will need a complete overhaul once the heavy equipment is out, so if you can aford a GEO chances are you will at least have to replace about 10 - 15 grand in landscaping.
    Well drilling company - about 2000 a hole 4-6 in at 150 feet down.
    Dive team for pond loop - about 120 an hour.
    Heavy equipment rental is around 1600 a week for a loader and backhoe.
    Glycol - lots of the alien slime.
    A mile of sheet metal for your air handling units.
    Lots and lots of time for tuning.
    2 in diameter pipes punching through your basement wall (real fun to work with especially when they are cold).
    The actual water to air units weigh a lot so heavy some of the bigger members of your crew handy.
    Low end Geo for a small home was about 30-40,000 dollars at 2500-4000 ft squared and about 65-120,000 dollars at 5000-12000 ft squared homes

    Just wanted to let you know some of the un-glorious things about GEO, it is a great idea, but not in the north for small companies trying to profit. Just a headache, schools make it seem great (mine did), but unless you are out trying to sell people this stuff and trying to put it in then I would not waste my time with my nose in a book trying to memorize calculations and practicing design principals. You need to find a local that does it, volunteer to help on a system and get your own perspective, I know after getting out of the HVACR design program at school and actually doing it I was left with a sour taste.

    But IGSHPA is the source for all GEO.
    have you read this thread or not?
    What lies behind us and what lies before us are small matters compared to what lies within us.


    Two pressures, four temperatures = SUCCESS!


    Boulder Heating Contractor


    For Consumers:

    For HVACR Professionals:


  20. #40
    Join Date
    Mar 2009
    Location
    mn.
    Posts
    38
    Post Likes
    I just got done reading this thread and I am now having second thoughts. I have a meeting with Water Furnace on Monday to become a dealer here in MN. and I don't know if this is even worth pursuing. I want to become a green contractor and sell things like this. But not if it is not going to make me any money or be a huge pita. Can any of you tell me if its worth trying or is it just a waste of my time, Thanks.

+ Reply to Thread
Page 2 of 3 FirstFirst 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •