    Myth or Fact?

    According to manuals,a compressor should not be bumped/started in a vaccum.I read a thread a while back that said the comp. could explode if stared in a vac.Is this true or false? PS:installed a new tecumsy cond. unit and while it was in vac,turned on breaker and it tripped.sounded like a dead short.also,compressor should not have started if system was in vac.(pressure control).checked the pins and compressor is open between all.220v/single phase.supplier is blaming my boss.what do you guys think?
    Artificial Intelligence is no match for Natural Stupidity

  2. #2
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    fact.

    scrolls can be nasty.

  3. #3
    Join Date
    Jun 2004
    Posts
    946
    Post Likes
    fact..

    u should not turn it on when its in a vacuum..

    when unit is in a vac the internal resistance will be a lot lower
    So if you turn it on it will usually jump from terminal to terminal direct short.

    if you are lucky it will be okay. if your lucky

  4. #4
    Join Date
    Jun 2004
    Posts
    946
    Post Likes
    if I was the suplier I would blame your boss too.

    you dont have to have both leg to short it to ground..

    sorry im with the supplier with this one

  5. #5
    Join Date
    Jul 2007
    Location
    regina saskatchewan
    Posts
    257
    Post Likes
    Thread Starter
    Thanks guys.
    Artificial Intelligence is no match for Natural Stupidity

  6. #6
    Join Date
    Oct 2001
    Location
    Stoney Creek, Ontario
    Posts
    885
    Post Likes
    i tried it once on a 15 hp discus, for the hell of it. took out compressor breaker, 2 of 3 200 amp fuses on rack, and 200 amp breaker in rack house. definately a dead short

  7. #7
    Join Date
    Sep 2006
    Location
    Chicago
    Posts
    491
    Post Likes
    Thats kind of an odd situation you got there. Ive seen more than 1 stuck closed pressure control take out a comp. But whats the point of throwing the breaker while its in a vacuum anyway. I wouldnt think it would take long for the motor to overheat and die with no load at all on it and no cooling. Plus I dont know that oil would make its way up to the cylinders when the systems in a vacuum?

  8. #8
    Join Date
    Nov 2008
    Location
    Altamont, IL
    Posts
    552
    Post Likes

    Frown Arc at Fusite

    I have been told that it can arc at the fusite (where the leads leave the compressor motor into the electric box) and burn it out,wasting the compressor
    In GOD We Trust

  9. #9
    Join Date
    Aug 2007
    Location
    Winter Haven, FL
    Posts
    4,380
    Post Likes
    The copeland manual states that applying power to compressor in a vacuum will burn fusite plugs.

    Why was the breaker turned on anyway? If you are trying to heat up the crankcase pull the compressor plug out before powering up.

  10. #10
    Join Date
    Dec 2006
    Location
    In a Mess
    Posts
    1,087
    Post Likes
    How much of a vacuum are we talking about before this carnage happens???? I've seen compressors run in their own vacuum due to a jumped pressure switch for a long time
    Sig removed by mod. G-Rated site

  11. #11
    Join Date
    Aug 2007
    Location
    Winter Haven, FL
    Posts
    4,380
    Post Likes
    It is probably on a compressor that has never been in use. Im sure some oil on the terminals has some insulating effect.

  12. #12
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,346
    Post Likes

    *

    it takes at least 3 things for an EXPLOSION

    fuel, spark, oxygen

    compression helps as well to make a nice explosion

    in a vacuum, there is no oxygen or compression

    so no, it won't explode



    .

  13. #13
    Join Date
    Jul 2008
    Location
    Denver, CO
    Posts
    4,379
    Post Likes
    I had a compressor start on me while it was in a 500 micron vacuum. The short was so bad it blew all 60 amp fuses coming into the RTU, triped the 80 Amp main breaker and weilded the contactor shut.

  14. #14
    Join Date
    Mar 2003
    Location
    Cochrane, AB
    Posts
    708
    Post Likes
    Quote Originally Posted by Airmechanical View Post
    it takes at least 3 things for an EXPLOSION

    fuel, spark, oxygen

    compression helps as well to make a nice explosion

    in a vacuum, there is no oxygen or compression

    so no, it won't explode
    .
    We're not talking combustion explosion here. A big spark by itself will blow the terminals out of the crankcase followed by oil. Then you may have a fire. Think of throw a nitro tank in a fire. No fuel or oxygen inside either, but will still explode.

  15. #15
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,815
    Post Likes
    http://202.56.127.90/nacg/ServiceBook/general.pdf

    Never saw an explosion yet but have seen

    terminal venting with what lawyers now call a "thermal event"

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •