    HVAC fire at our Cabella's this week...

    Not much damage done to the store other than some minor smoke and water. I have no inside info yet of what caused the fire other than the smoke got let out of something in the RTU.

    Looks to me like it started in the controls cabinet, maybe a faulty controller or a loose wire?

    FWIW it's a York unit, not sure what model though.
    Click here to see the picture of Mr Roasty
    "If you call that hard work, a koala’s life would look heroic."

  2. #2
    Join Date
    Jan 2009
    Location
    Indiana
    Posts
    3,228
    Post Likes
    do i see the disconnect is still on? If they want that unit re weird they better turn that off.

  3. #3
    Join Date
    Mar 2005
    Posts
    12,994
    Post Likes
    You coulda buffed that right out.

    Who was the last one to wrench on it?

  4. #4
    Join Date
    Jun 2000
    Location
    B.C. Canada
    Posts
    147
    Post Likes
    That looks like the High Limit did not work when the blower stopped working, I have seen this before and that's what had done it, only someone wired out the limit so it didn't work.

  5. #5
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    28,074
    Post Likes
    Quote Originally Posted by Juleous View Post
    That looks like the High Limit did not work when the blower stopped working, I have seen this before and that's what had done it, only someone wired out the limit so it didn't work.
    ...and the heat caused an electrical short near that compressor contactor, and the current was below the protection value, but enough to add a lot of electrical burning.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  6. #6
    Join Date
    May 2004
    Location
    Rapid City, SD
    Posts
    7,416
    Post Likes
    Thread Starter
    This building was completed this spring I believe, possibly late last winter. I'm sure it's had some run time on it in the heating mode, but not too much, so this cold snap we had was likely one of the 1st.

    The company that installed it does good work and their service guys are pretty dang good too, so I doubt it was anything fouled up by a poor tech. Perhaps it was just one of those things.

    Kinda makes you realize how important our job can be though.
    "If you call that hard work, a koala’s life would look heroic."

  7. #7
    Join Date
    Apr 2004
    Location
    Muskegon, Mi.
    Posts
    425
    Post Likes
    Must be a product de mexico.

  8. #8
    Join Date
    Oct 2009
    Location
    Cleveland
    Posts
    21
    Post Likes

    Confused York

    Had a York start on fire on me last winter in heat start up mode unit running fine everything looked cool.contacted york and was told they had an issue with 6 ton and less with high limit not opening and catching unit on fire since then if you order new high limit it comes with aux limit and new harness
    York released no service letter that i know of

  9. #9
    Join Date
    Nov 2004
    Location
    Skokie , IL near chicago
    Posts
    1,197
    Post Likes

    Confused hey mr builder......

    Quote Originally Posted by timebuilder View Post
    ...and the heat caused an electrical short near that compressor contactor, and the current was below the protection value, but enough to add a lot of electrical burning.
    you got there first with what i was gonna say , the last time i saw anything like that was when an electrical contractor ran like a 200 amp service to a 15 t rooftop with full sized fuses in it and it just burned so bad the brass contacts in the contactors melted an hardened like little raindrops inside the cabinet......Jack