    Question Excessive water use by cooling tower, need some help

    Have an issue whereas we are using a lot of water (cut off the water supply and the water meter just about stopped - went fron 60 GPm to 4 GPM). Any ideas what can be happening??? Thanks!

  2. #2
    Join Date
    Aug 2006
    Posts
    3,048
    Post Likes
    Hire a Pro to look at it !!
    I only have to make it work till I retire.

  3. #3
    Join Date
    Oct 2009
    Posts
    2
    Post Likes
    Thread Starter
    Thanks Madhat, but we've had two different companies look at it with no avail. Either the system is too complicated for the "professional" commerical HVAC company or they couldn't find the problem. Thanks again for your response and help with this.

  4. #4
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,625
    Post Likes
    You gotta admit, j, that your request looks a bit odd, especially considering the lack of pertinent info about the problem. If you want an opinion as to why a device that is supposed to use water is using more water than you think it should, then you'll have to post all of your operating and design information for folks to look at. There's another thread not too far from here on this same subject - it might be of help. Otherwise, all anyone can tell you is that normal evap rate on a cooling tower is 1.5 + gph/ton, not counting bleed-off or carry over.

    It would also be nice for you to put something about you in your profile so we know who you are. Based on your response to madhat, I can tell you that this is not a DIY site.

  5. #5
    Join Date
    Aug 2006
    Posts
    3,048
    Post Likes
    56 gallons x 60 min x 24 hours = 80,640 Gallon a day A 15' x 30' x 4' average depth backyard pool holds 13,500 gallons, unless your secretly running a Nuclear Power Plant that's a lot of water.
    Last edited by madhat; 10-15-2009 at 10:19 AM. Reason: left out wording
    I only have to make it work till I retire.

  6. #6
    Join Date
    May 2008
    Location
    Central Pennsylvania
    Posts
    630
    Post Likes
    Quote Originally Posted by madhat View Post
    56 gallons x 60 min x 24 hours = 80,640 Gallon a day A 15' x 30' x 4' average depth backyard pool holds 13,500 gallons, unless you running a Nuclear Power Plant that's a lot of water.

    That comes out to about a 1866 ton cooling tower if my calculations are correct.

    3 gpm per 100 tons, 56 gpm / 3 = 18.66, 18.66 X 100 = 1,866 TR

    That means theres got to be something good hooked to that tower, I'll come look at it for ya!

  7. #7
    Join Date
    May 2006
    Location
    N.E. IA
    Posts
    525
    Post Likes

    Hmm

    Quote Originally Posted by j28 View Post
    Have an issue whereas we are using a lot of water (cut off the water supply and the water meter just about stopped - went fron 60 GPm to 4 GPM). Any ideas what can be happening??? Thanks!
    Float broke off the fill valve and water flowing out the overflow drain.????????????
    "Wheel" mechanics work on "Wheel" chillers

  8. #8
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,733
    Post Likes
    Man, the title of this thread threw me for a loop. On the list it says the chiller is using excessive water, which made me go "ruh roh". I click on the link only to learn it's the cooling tower, not the chiller. Still a "ruh roh", anyway.

    Find the tower overflow exit point and see if it's gushing water. Your tower conductivity level should also be through the floor if you're making up a lot of water. Both are clues of make-up float valve problems.

    If you have one GPM or water meter feeding all of your towers (if there's more than one) you can cut the water supply off to each tower (provided there's a shutoff valve at each tower make-up valve) to see which one is using a lot of water.
    Building Physics Rule #1: Hot flows to cold.


    Building Physics Rule #2:
    Higher air pressure moves toward lower air pressure


    Building Physics Rule #3:
    Higher moisture concentration moves toward lower moisture concentration.

  9. #9
    Join Date
    May 2001
    Location
    Western Wa
    Posts
    2,363
    Post Likes
    The first thing to look at is the fill valve or fill valves if you have more than one.
    You might be running over into the overflow and just don't see it.

    A cooling tower will use anywhere from 1.6 to 2.2 gallons per hour per ton, depending on a lot of variables like incoming water quality, and how many cycles of concentration your water treatment can handle before solids start precipitating out on the condenser tubes.
    God Bless our Veterans

    God Bless the USA

  10. #10
    Join Date
    Nov 2006
    Location
    US
    Posts
    112
    Post Likes
    I call this pissing in the wind, it doesn't say what make up water is hooked to, is it the tower or is it the evap side???(big leak) need a lot more details including tonnage of equipment, and how do you still have 4 gpm with make up off

  11. #11
    Join Date
    Dec 2008
    Location
    Upper Peninsula,Michigan
    Posts
    38
    Post Likes

    Talking

    Quote Originally Posted by shophound View Post
    Man, the title of this thread threw me for a loop. On the list it says the chiller is using excessive water, which made me go "ruh roh". I click on the link only to learn it's the cooling tower, not the chiller. Still a "ruh roh", anyway.

    Find the tower overflow exit point and see if it's gushing water. Your tower conductivity level should also be through the floor if you're making up a lot of water. Both are clues of make-up float valve problems.

    If you have one GPM or water meter feeding all of your towers (if there's more than one) you can cut the water supply off to each tower (provided there's a shutoff valve at each tower make-up valve) to see which one is using a lot of water.
    Very good analysis...I agree..

  12. #12
    Join Date
    Feb 2010
    Location
    Ontario, Canada
    Posts
    15
    Post Likes
    Quote Originally Posted by j28 View Post
    Have an issue whereas we are using a lot of water (cut off the water supply and the water meter just about stopped - went fron 60 GPm to 4 GPM). Any ideas what can be happening??? Thanks!
    The guy's are right Poster. You need to give more info including what part of the world this piece of equipment is in. M#'s etc. Your profile is also very sparse.

  13. #13
    Join Date
    Jul 2008
    Location
    Washington, DC
    Posts
    1,587
    Post Likes
    Quote Originally Posted by j28 View Post
    Have an issue whereas we are using a lot of water (cut off the water supply and the water meter just about stopped - went fron 60 GPm to 4 GPM). Any ideas what can be happening??? Thanks!
    Do the pipes between the chiller and the tower go underground?