Page 2 of 2 FirstFirst 12
Results 14 to 17 of 17

Thread: Chiller Load

  1. #14
    Join Date
    Jul 2009
    Posts
    10
    Post Likes
    I'll check the stpts in the morning but I know softload is on @ 300sec, min capacity is 10% 30min timer, and the differential to start is +-5. it just boils down to the load we need it.

  2. #15
    Join Date
    Apr 2004
    Location
    Winnipeg,MB,Canada
    Posts
    102
    Post Likes

    chiller cycling

    What is the volume of your chilled water loop, it should take at least five minutes for the water to get around the loop.
    The volume of water divided by the flow rate, should equal more than five. If you don't, a large storage tank could help the situation.

  3. #16
    Join Date
    Jul 2009
    Posts
    10
    Post Likes
    Any idea how to determine the loop volume?

  4. #17
    Join Date
    Apr 2004
    Location
    Winnipeg,MB,Canada
    Posts
    102
    Post Likes

    loop volume

    How many feet of what diameter of what type of pipe? length x area=volume, volume of heat exchangers, etc.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.
Comfortech 365