    Jul 2009
    I'll check the stpts in the morning but I know softload is on @ 300sec, min capacity is 10% 30min timer, and the differential to start is +-5. it just boils down to the load we need it.
    Winnipeg,MB,Canada
    chiller cycling
    What is the volume of your chilled water loop, it should take at least five minutes for the water to get around the loop.
    The volume of water divided by the flow rate, should equal more than five. If you don't, a large storage tank could help the situation.
    Jul 2009
    Any idea how to determine the loop volume?
    Winnipeg,MB,Canada
    loop volume
    How many feet of what diameter of what type of pipe? length x area=volume, volume of heat exchangers, etc.