Results 1 to 7 of 7
    Aug 2009
    Fine Tune Refrigerant Charge - on warm day only?
    A contractor told me that he would return in the spring when the temp was 75 degrees to fine tune the refrigerant charge on his proposed system. Is this necessary?
    Also, if the lineset is replaced does a line drier still have to be installed?
    Thanks!
    pittsburgh,pa
    That is how i install a/c in the colder months if possible. A drier should be in the new unit purchased or one should be added if the system is open for repair.
    "Can't see it from my house"
    Oct 2009
    New Jersey
    That's the way to get the best performance from your AC system.
    Austin, TX
    A drier should be someplace in all new systems. Sometimes driers are built into the AC condenser unit by manufacturers. In these situations you won't have an external filter drier.
    It's hit or miss to get the refrigerant amount right when the outdoor temp is lower than 60 degrees. The manufacturers technical data doesn't go that low. Sounds like your installer is willing to go the extra mile to make sure your system is running right.
    “I am for doing good to the poor, but...I think the best way of doing good to the poor, is not making them easy in poverty, but leading or driving them out of it. I observed...that the more public provisions were made for the poor, the less they provided for themselves, and of course became poorer. And, on the contrary, the less was done for them, the more they did for themselves, and became richer.”
    ― Benjamin Franklin
    Dec 2008
    Buffalo NY
    Cool Thats the best way
    That is the way I do it also. It is better to come back and make sure it is perfect. A drier is usually installed in most of the newer condensors already.
    To the man who always did it right. I love you dad and I will miss you to much for words.
    Stay Thirsty My Friends
    Support the Skilled Trades Don't DIY
    Oct 2009
    belleville IL.
    sounds like a GOOD inataller to me ,on those issues any way .
    Northeast Ohio
    We always do a return check on systems installed in the off season. The factory charge is normally right on but adjustments still need made because of line length. Power also needs to be applied to the outside unit several days before the run test (breaker on)