PUP Input Override in Tridium AX
Controller Type HX - Pup network to AX
I am trying to get the sensor to allow override, I drag the Analog Input Subchannel 2 (attribute "CV", Type "fe") into my points list, and then go to properties sheet, and change PreWrite Attribute to "Oi", sensor always says "Read fault: could not determine override state; Write fault: unable to set override or manual".
Any suggestions?
I set attribute DT to "254", and same problem.
I have played with Main Analog Input Channel "OI" Attribute also, no luck.
Every other feature works, just hung up on this one issue.Intelli-Building = Less Stress, commissioned with diligence!
-
10-12-2009, 11:02 AM #2
Professional Member
- Join Date
- Dec 2007
- Location
- Connecticut
- Posts
- 748
Try bringing in the OI attribute as a separate boolean writable. I think you will need to make the FE02:CV a numeric writable as well.
-
10-14-2009, 12:09 AM #3
-
10-14-2009, 09:14 AM #4
Professional Member
- Join Date
- Dec 2007
- Location
- Connecticut
- Posts
- 748
I mean the OI attribute on FE02. That should be what you need.
-
10-14-2009, 11:44 AM #5
I finally got it to work, on the HX controller, they do not have a CV & OI in same channel, thus I could not use the "Oi" feature in property view for the CV. So I set up an Override Button, then a CHANGE VALUE button with action.
Now my only issue yet is the clock value in the HX is the value of my time zone, less the offset, in other words it's about 6 hrs off.Intelli-Building = Less Stress, commissioned with diligence!