[QUOTE=AtoZhvac;4724222]Hi,
AtoZhvac
"Another thing say you are charging an R22 refrigeration system (large pan cooler) which requires 34 pounds of R-22. I had a heck of a time getting that much charged in. I ran warm water over the container many times to get the pressure back up to charge in the vapor."
It would not take long to charge 34lbs R-22 through liquid line
-
10-17-2009, 10:17 PM #15
-
10-17-2009, 10:22 PM #16
-
10-17-2009, 10:25 PM #17
-
10-17-2009, 10:31 PM #18
-
10-17-2009, 10:54 PM #19
What I was meaning is that without low ambient conditions the additional refrigerant would not be needed. Sporlan's charging procedures first show you the proper charge of refrigerant needed without low ambient conditions. Under those conditions a receiver would not really be needed, so that charge should be able to be stored in the condenser in a pump-down. Next sporlan directs you to weigh in the additional refrigerant needed for low ambient conditions into the "high side";which is really why the receiver tank is there-to store the extra refrigerant needed for low ambient conditions. Therefore the normal charge should be able to be "stored" in the condenser at pump-down, alllowing you to weigh in the additional low ambient charge in the receiver that has been isolated from the condenser in a pump-down.
-
10-17-2009, 10:58 PM #20
Normally, I just charge into the suction line, as I said before.
-
10-17-2009, 11:07 PM #21
I understand what your saying. I was just hoping someone would answer the question about what spolan means by weighing in the charge on the high side. Being on a roof at 10 degrees when its snowing and windy at night and having to weigh in 10 lbs of refrigerant by "metering" it in on the low side can be hell. 10 lbs of liquid dumped in on the high side in a vaccume(?) would get you out of there in a minute.
-
10-18-2009, 12:14 AM #22
Professional Member
- Join Date
- Oct 2007
- Location
- ATLANTA
- Posts
- 120
-
10-18-2009, 12:24 AM #23
Professional Member
- Join Date
- Oct 2007
- Location
- ATLANTA
- Posts
- 120
-
10-18-2009, 12:52 AM #24
-
10-18-2009, 12:54 AM #25
No it is not. The receiver would have to have a service valve at the inlet that you could close to separate it from the high side. Just like a residential condensing unit. After that the unit will go into a pump-down just as when the liquid line solenoid valve closes when the unit is satisfied on temp. Except in this case you have stopped all liquid from entering the receiver, so the liquid has to be storred in the condenser-just like a residential pump down. This would place the receiver in a vacume.
-
10-18-2009, 01:05 AM #26
Are you talking about just committing suicide and personally sucking that liquid refrigerant in or committing murder to the compressor by letting it suck straight liquid in? I'm guessing you mean metering in the liquid in to the suction line. Still, that can be time consumming.