Page 8 of 9 FirstFirst 123456789 LastLast
Results 92 to 104 of 116
  1. #92
    British Columbia, Canada
    I gotta say I'm impressed with your patience and restraint JP.
    From reading this thread from start to finish I was sure that someone was pulling your chain but when I got to the point where they both stated that they were drinking I almost fell off my chair I was laughing so hard.
  2. #93
    Jan 2010
    Plus this thread is almost four years old.
  3. #94
    I was far more restrained 4 years ago...
  4. #95
    Jan 2013
    I have a Bailey walk-in freezer.... How would I calculate the amount of refrigerant needed for this system?
  5. #96
    Jan 2013
    the link http://sporlan.jandrewschoen.com has expired....
  6. #97
    You could measure all the tubing in the system piping and both coils and calculate the internal volume. Then work out where there would be various vapor volumes at the various pressures. And so forth.
    Or you could look up the total receiver volume for the system refrigerant and then use 75% of that as the charge. If you have to bid the job - use 100%. <g>
    I have worked on systems which could not be pumped down - but not very many.
    PHM
    Quote Originally Posted by cthegreat1 View Post
    PHM
  7. #98
    No it's not. I just posted so it's a current thread. Perhaps you meant to say that this thread had it's genesis almost four years ago? <g>
    PHM
    PHM
  8. #99
    Jan 2010
    Quote Originally Posted by Poodle Head Mikey View Post
    PHM
    Ahhhh. No I'm sticking with the fact that this thread is almost four years old. Now the POSTING are recently current but the thread at it's genesis is approaching four years of age.
  10. #101
    Oct 2007
    Oh yeah.
    This is what I do. Seemed like common sense at the time. First charge as much liquid as you can through the liquid side, and then throttle it in with the gauges at 5-10 psi over the system suction pressure to top it off.
    Always worked like a charm.
    Oh, and BTW - I never use a digital gauge. Just seems to make me lose touch with whats goin' on. I dont even use a digital vacuum gauge - but instead I collect (yes, I have 4) of the Thermal Engineering vacuum gauges. They are ridiculously cheap if you can find them.
    Maybe I am just too much of an ole codger
    BTW - looks like ALL of those Sporland links are ded.
    One of the best kept secrets in the HVAC/R business must be that all refrigerant gets charged as a liquid. <g>
    Who the hell has the time to warm the cylinder repeatedly and then wait for pounds and pounds of refrigerant to boil off? Don't your service managers scream over all the time you are taking?
    There are little vaporizing widgets you can charge through but why not just crack the suction side gauge handle and let it boil/vaporize in through the crack? If you are very curious (as I was <g>) use two 1/4" flare MxF sight glasses. Put one before the suction hose - screw it onto the left bottom side of your gauge set - and put the other one onto the suction access flare on the unit. Then crack the suction gauge manifold handle a little and see what the refrigerant looks like in the sight glasses.
    With the manifold gauge cracked - tell me what you see.
    And also note the suction pressure increase on your gauge (valve open versus valve cracked) initially 'set' it for 5-10 lbs over running suction pressure. Use an analog gauge and watch the needle flutter. If the needle is steady the gauge valve is either open too far or closed too much. <g>
    PHM
  11. #102
    Oct 2007
    Except its not really a secret. Some folks just dont read
  12. #103
    Quote Originally Posted by lexscripta View Post
    Yeah, I've realized that.
    http://sporlanonline.com/literature-...lating-valves/
    Look there for more Sporlan info
  13. #104
    Sep 2011
    I guess the bottom line is if there is a head pressure control the charge must be calculated? You cant just charge based on subcooling like any other system?
    If i came to a system and was unsure i it was properly charged, i would remove recover refrigerant until i saw bubble and then topped it off following sporlans procedure?
    P.S. i have only charged two systems with vapor (the first two systems i ever charged) the rest? Always liquid to the suction. I cant imagine doing it any other way with exception of through the liquid service valve.
