    York YTG1A1B2-CGJ Machine. Optiview panel was blank upon arrival. I unplugged J15 from the microboard and reconnected. Optiview came up and went to working. Started chiller and all was well. Anyone ever seen this?
    It might get loud!

  2. #2
    Join Date
    Dec 2006
    Posts
    39
    Saw that happen once and it ended up being a black plug/fuse on the microboard came loose. Pushed back in and the screen was back on.

  3. #3
    Join Date
    Jun 2008
    Location
    Houston, TX
    Posts
    48
    if it continues to happen there is an updated power supply harness from the power supply to the micro

  4. #4
    Join Date
    Jan 2009
    Location
    Jersey
    Posts
    119
    also check your sensors. the 5vdc is very sensitive on the optiview. if a senor pulls the voltage down below 4.8vdc the panel goes into safety mode and shuts down. I've seen temp sensors or pressure transducers do it at high end of measuring range.

  5. #5
    Join Date
    Feb 2006
    Location
    SouthEastern Virginia
    Posts
    1,012
    Anyone have a service bulletin regarding this issue?
    It might get loud!

  6. #6
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,446
    Nope just good old fashion troubleshooting. ( now thats using your dip stick jimmy ).
    Arguing with your Boss is like wrestling with a pig in
    mud.
    After a while you realize that while you are getting
    dirty, the pig is actually enjoying it.

    It is not exactly cheating, I prefer to consider it
    creative problem solving.

  7. #7
    Join Date
    Feb 2006
    Location
    SouthEastern Virginia
    Posts
    1,012
    Gee thanks for the help York56.
    It might get loud!

  8. #8
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,446
    I have never seen any bullitins on it , some of the things mentioned are possible causes , power supply , connections , ribbons , defective componants pulling down power all things to look at process of elimination
    didn't mean to be sarcastic.
    Arguing with your Boss is like wrestling with a pig in
    mud.
    After a while you realize that while you are getting
    dirty, the pig is actually enjoying it.

    It is not exactly cheating, I prefer to consider it
    creative problem solving.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •