Results 1 to 9 of 9
Thread: York YCAS250 Microprocessor Help
10-15-2009, 11:03 AM #1
Installing a new board in chiller. I tried to program the 21 different menus and can find only 14. The chiller will run a comp for about a min. and then go off on over amp because one of the menus I cant find is motor current setting. Do I need to set a dip switch to get to these additional 7 menus? I have used the password given in the IOM (7396) and also the York password (9675). Still cant find.
You are who you are and where you are because of what you think.
10-15-2009, 11:35 AM #2
- Dec 2006
- 39
There is a another secret code and i am trying to remember it as I type. This code will get you into the screen you need, i then right down the specs on the inside of the panel. Try 5244??? Get right back to me and let me know, i'm starring at my phone trying to remember.
10-15-2009, 11:40 AM #3
- Dec 2006
- 39
or try 5422, i am real close.
10-15-2009, 11:43 AM #4
- Dec 2006
- 39
try 5144, i keep looking at the numbers on the phone to remember the sequence.
10-15-2009, 11:59 AM #5
I got rained off the job. I will let you know if any of those worked. Thanks for the info.
10-15-2009, 04:04 PM #6
Professional Member*
- Dec 2008
- Dixiana, AL
- 2,499
5144
10-15-2009, 04:21 PM #7
We got a winner. 5144. Thanks for the info guys.
10-15-2009, 04:26 PM #8
The code Klove gave is the correct one if you changed the micro board or expansion module you will need the set the motor protection info. back up as you are already experiencing problems due to that.
Arguing with your Boss is like wrestling with a pig in
mud.
After a while you realize that while you are getting
dirty, the pig is actually enjoying it.
It is not exactly cheating, I prefer to consider it
creative problem solving.
25 years ago we had Bob Hope , Steve Jobs , and Johnny Cash today we have no Hope no Jobs and no Cash !
10-16-2009, 07:16 AM #9
- Dec 2006
- 39
Right on!!! Glad it worked!!!