DP across modulating steam valve
Looking for some sage input on the following...
25psi inlet steam to a modulating steam valve with a 195 #/hr load. I've calculated this application to require a 3.32cv valve. I can only get a 2.2cv valve or a 4.4cv valve.
So, my question is this: does anyone have a calculation to determine DP on a steam valve knowing these variables: valve actual cv, steam load, and inlet pressure.
I need to know the theoretical DP with the two valve options so I can pick the lesser of two evils. Otherwise the choice between the valves is arbitrary. But all steam valve sizing calculations I can find only compute CV when you have a desired DP, and not the other way around.
Thanks for any input, and please correct my thinking if I'm approaching this incorrectly.
-
10-06-2009, 03:37 PM #2
Professional Member
- Join Date
- Jun 2009
- Location
- StL, MO
- Posts
- 532
Try this calculator.
http://www.controlpix.com/steamvalve.htmlUA LU 562
-
10-06-2009, 03:44 PM #3
Regular Guest
- Join Date
- Apr 2006
- Location
- New England
- Posts
- 189
Thanks, that's exactly what I was looking for.