no heat question
everything starts up fine on gas furnace except: ventor motor starts,ignitor lights up, gas valve clicks open,here and smell gas going to burners,but no ignition...repeats this process...not sure how to fix this...i cleaned burner orifices,and gas burners,,no luck..will ignitor still glow,if it is faulty,,any help appreciated,,thanx..
-
10-04-2009, 12:33 PM #2
You should get you one of those Edenpures I here they don't cost much to run and they never break down.
-
10-04-2009, 12:35 PM #3
Maybe still air in gas line?
I'm not tolerating Political Correctness anymore, from now on it's tell it like it is.
Veto Pro Pak - The best tool bag you'll ever own
-
10-04-2009, 01:33 PM #4
Professional Member
- Join Date
- Nov 2004
- Posts
- 1,009
I do not think we can help you. I suggest you call a licensed HVAC contractor to help you in your situation
-
10-04-2009, 01:47 PM #5
The vaule should not open till it get enough heat or spark to light the pilot.
Last edited by beenthere; 10-04-2009 at 07:43 PM. Reason: Deleted DIY info from quote
THE MORE I LEARN
THE MORE I FIND I DONT KNOW
Cancer Survivor
And Dam Well
Plan On Staying That Way
-
10-04-2009, 02:16 PM #6
You are playing with Fire
call someone
this is not a DYI site sorryTHE MORE I LEARN
THE MORE I FIND I DONT KNOW
Cancer Survivor
And Dam Well
Plan On Staying That Way
-
10-04-2009, 06:24 PM #7
Professional Member
- Join Date
- Mar 2007
- Location
- Chicago
- Posts
- 45
1) Thermostat calls for heat
2) Draft inducer fan turns on and runs for maybe a minute
3) Hot surface ignitor turns on and stays yellow-orange color for 20-30 seconds
4) Relay on fan control board clicks
5) Gas valve opens a fraction of a second later (verified by dial pressure gauge)
6) If flame is established, ignitor powers down after a few seconds, gas valve stays open, and furnace runs until thermostat is satisfied
the gas valve will open to try and ignite the burners, if the ignition is not hot enough this will not happen.
-
10-04-2009, 06:28 PM #8
Professional Member
- Join Date
- Mar 2007
- Location
- Chicago
- Posts
- 45
-
10-04-2009, 06:30 PM #9
-
10-04-2009, 06:55 PM #10
Professional Member
- Join Date
- Nov 2004
- Posts
- 1,009
well if he is "lisenced" I still wouldn't want him to look at my system.
Now a "licensed" tech I would allow to look at my system.
We Do not give out tech advise with out first knowing the poster.
HVACR equipment is dangerous and can KILL, INJURE, BLOW THE PLACE UP ETC.
-