    Do you guys change the compressor sump oil each year or rely on oil analysis?
    North America
    I do it after the first year. Then do an oil sample every year and change the oil every 3 after that. Due to the fact the were not running in a vacuum and drawin in moisture or at least shouldnt be depending on your running conditions.
    Dec 2008
    Dixiana, AL
    Quote Originally Posted by hvacr View Post
    This is a good way to keep track that hvacr uses.
    My method is 5,000 hours after commissoning, every 30,000 afterwards unless analysis says sooner. All filters yearly. As well as what was mentioned about no air ingress into the machine (except in the event of poor service practice or pure accident), synthetic oil doesn't break down with use as readily as mineral oil.
    May 2008
    Thanks for the info guys. I'm going fishin so we'll have to continue this discussion on Monday. Have a good weekend.
    pennsylvania
    oil analysis. who do you work for 81?
    May 2008
    LT,
    Thanks for the input. I work for one of the larger MC's in central Pa, don't want to say much more than that over an open forum. I tried PMing you but couldn't, I guess you have to be a pro member to receive PM's, you should get signed up so you can receive the other benefits of this great site. Are you from the area?
    Oregon
    We don't ever change it but oil analysis is always good, also emptying the seal bottles every few days helps.LOL
    Federal Reserve, stealing your kids futures since 1913
    UA290
    pennsylvania
    Quote Originally Posted by chillerguy81 View Post
    LT,
    i am from the area. work from harrisburg to n.y. and bloomsburg to huntington
    May 2008
    Quote Originally Posted by largetonnage View Post
    Ah we're practically neighbors, I'm normally within a two hour radius of H-burg.