    Manual J formulas?

    I've got all the software I need but what I'm looking for is a book or something where I can find the actual formulas & factors used for calculations. What I need is a form sheet where I put my sq. ft. walls,widows etc..& then gives me the factors needed to multiply where I have to calculate each item seperately instead of the program doing it for me. Years ago before computers I had a book that I used to do my load calculations with .
    I've been learning a little javascript & I'd like to give it a try but I need to be able to do a calculation manually before I begin.
    Any ideas?

  2. #2
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Post Likes
    Quote Originally Posted by garyed View Post
    I've got all the software I need but what I'm looking for is a book or something where I can find the actual formulas & factors used for calculations. What I need is a form sheet where I put my sq. ft. walls,widows etc..& then gives me the factors needed to multiply where I have to calculate each item seperately instead of the program doing it for me. Years ago before computers I had a book that I used to do my load calculations with .
    I've been learning a little javascript & I'd like to give it a try but I need to be able to do a calculation manually before I begin.
    Any ideas?
    www.acca.org

  3. #3
    Join Date
    Sep 2002
    Location
    I don't know
    Posts
    3,022
    Post Likes
    Q Loss (BTUs) = Surface area x (indoor - outdoor design temp) / Effective R-value*

    *You have to take thermal bridging through studs into consideration - an R12 wall has a real thermal resistance value of less than R12.

    The R value of basic wood double pane windows is around 1.7 if I remember correctly.

    For air leakage:

    Q sensible (Btus) = 1.09 x airflow CFMs x (indoor - outdoor design temp)

    A blower door test is required to measure leakage.

    I don't know the formula for latent heat loss off the top of my head.

    Don't worry about passive solar heat gain for heating since the system has to be sized for design conditions. (No sunlight)

    For making a template I recommend excel.