    Humidity Eating Machine

    I have a challenging project here, constant volume of air for high fitlration rates, a high amount of outside air and I have to maintain 68F and humidity in the 50 to 60% range. No outside walls, no roof, no external heat gain.

    So I am using a custom chilled water air handler with a built in 7.5 ton dehumidifer.

    Had to have it built in two pieces it has to fit through existing mechanical room doors.



    This is the coil section, you can see the 2.5" coil connections for a chilled water coil in the back. The coil visible in the front is a heresite coated condenser-reheat coil



    This is a DX evaporator coil which is down stream of the chilled water coil and upstream of the condensing coil



    This is the compressor, it turns on when there is a call to dehumidify, its DX coil gets air down to about a 48 dew point, the condenser coil reheats the air and when combined with the heat the fan and motor add, it will supply air at 65F with the low dewpoint.




    Blower Section



    BAF fan and 15 hp Premium efficiency motor - there are external filter banks in the duct work, fan will be up against about 6 inches of total static
    The way we build has a greater impact on our comfort, energy consumption and IAQ than any HVAC system we install.

    http://www.ductstrap.com/

  2. #2
    Join Date
    Aug 2006
    Location
    Ohio
    Posts
    2,572
    Post Likes
    Sweet.

    What is this "heresite" coating that you speak of? What does it do?

  3. #3
    Join Date
    Apr 2002
    Posts
    11,808
    Post Likes
    Thread Starter
    heresite is a corrosion protection coating

    I deal with salt air problems down here, this unit has a lot of outside air on it
    The way we build has a greater impact on our comfort, energy consumption and IAQ than any HVAC system we install.

    http://www.ductstrap.com/

  4. #4
    Join Date
    Jun 2004
    Location
    4H: Hot, Humid Houston H.O.
    Posts
    3,304
    Post Likes
    I am pretty impressed. Thanks for posting the pictures and description. Maybe you should publish a paper on this problem and its solution?

    Regards -- Pstu

  5. #5
    Join Date
    Nov 2008
    Location
    S.C.
    Posts
    991
    Post Likes
    I would love some of that. I have done a few similar to this at the hospital. I love that type of work, every now and then.

    Let's see some pictures during and after the install, PLEASE

  6. #6
    Join Date
    Apr 2002
    Posts
    11,808
    Post Likes
    Thread Starter
    its up and running now 3/4 commissioned. I expect to get complaints it is too dry in there now

    It is not under a full load yet, was sized for a bit of an expansion. So far holds about 69F and 40% RH. I can drop the temperature it maintains easy enough, I can also raise the humidity as well.

    There will be an increase in fresh air on it in the near future, I figure it will naturally hunt towards 50% RH

    When it goes into dehumdifying mode it blows 65F bone dry air. This is all internal loads so space temp will hold about 6 degrees higher than the supply air temperature at the moment.

    I use the dehumidifier as a reheater when it gets to cold in there as well. So the 'warm it back up' function at the moment is pushing RH down low.

    So if it gets too humid it blows dry 65F air, it gets too cold, it blows dry 65F air.
    The way we build has a greater impact on our comfort, energy consumption and IAQ than any HVAC system we install.

    http://www.ductstrap.com/

  7. #7
    Join Date
    Apr 2002
    Posts
    11,808
    Post Likes
    Thread Starter
    right now it will blow air with a 48 dewpoint on demand. If they drop the chiller temperature I can get a 45 dew point.
    The way we build has a greater impact on our comfort, energy consumption and IAQ than any HVAC system we install.

    http://www.ductstrap.com/

  8. #8
    Join Date
    Apr 2002
    Posts
    11,808
    Post Likes
    Thread Starter
    Quote Originally Posted by pstu View Post
    I am pretty impressed. Thanks for posting the pictures and description. Maybe you should publish a paper on this problem and its solution?

    Regards -- Pstu
    See I use dehumidifiers when they are needed

    I worked for this particular manufacturer back in the day, mainly in the design department. This is about the thrid project I have done with them down here with the hot gas reheat scheme.

    York has roof top units that do something similar, except they blow air about a degree or 2 warmer than they draw in in this situation. I have used them here.

    Bard offers a similar set up in their wall mounted units, I have used them here as well.

    I like the scheme because you use the energy you pay for twice.
    The way we build has a greater impact on our comfort, energy consumption and IAQ than any HVAC system we install.

    http://www.ductstrap.com/

  9. #9
    Join Date
    Apr 2002
    Posts
    11,808
    Post Likes
    Thread Starter
    an extra coil, a solenoid and an extra refrigeration line and could do the same thing to a house, it would eat up a little more fan power though
    The way we build has a greater impact on our comfort, energy consumption and IAQ than any HVAC system we install.

    http://www.ductstrap.com/

  10. #10
    Join Date
    Apr 2002
    Posts
    11,808
    Post Likes
    Thread Starter
    condensate is coming out at about 0.4 GPM, that adds up over the course of 24 hours
    The way we build has a greater impact on our comfort, energy consumption and IAQ than any HVAC system we install.

    http://www.ductstrap.com/

  11. #11
    Join Date
    Jun 2004
    Location
    4H: Hot, Humid Houston H.O.
    Posts
    3,304
    Post Likes
    Very interesting. What wattage does it draw at that rate of work?

    Thanks -- Pstu

  12. #12
    Join Date
    Apr 2002
    Posts
    11,808
    Post Likes
    Thread Starter
    hard to say pstu, 15 hp blower motor, the chiller does a big chunk of the work

    But this is a project that needs reheat because of pyschrometric reasons, and the condenser heat doubles as the reheat, rather than burning fuel or using electric heaters

    I removes well over '4000 pints per day', compared to the electric reheat alternative, it pays for it self fast, in less than a year on 24/7 operation
    The way we build has a greater impact on our comfort, energy consumption and IAQ than any HVAC system we install.

    http://www.ductstrap.com/

  13. #13
    Join Date
    Aug 2006
    Posts
    3,048
    Post Likes
    What, no Desiccant dehumidifing



    BTW, still can't get desiccant dehumidifier to work, they want 50 to 85% (Adjustable by lab personal) at 4.0 C. Wondering if this is even possibly, as no ones desiccant graph goes this low.
    I only have to make it work till I retire.