    WMC

    If it's a WMC then it has an electronic expantion valve, need to set the gain up, when chiller is at 100% too maintain design approch, which is about 1.5 'F, set the Slop up too perform the same Approch at light loads, Like 20%. this setting is on the unit Controller set points