Results 1 to 13 of 14
Thread: WMC
    North America
    WMC
    Hello,
    I hace a WMC aprox 135 ton single comptrssor. It has been tripping on Low evap pressure. I live in the north and its cool. The tower is controlled from chiller and is single fan driven by VFD. What should the lift be set up to default is 30 i think. Is there a upper limit. I was wondering also if I lower the min amps below 10% as long as I keep motor cooling.
    I would like to raise the lift as the condenser sightglass is full and evap is empty and I think were stacking refrigerant in the condenser. It has tripped off on Low evap pressure a few times.
    Jul 2009
    In a mechanical room....
    Whats your super heat and sub cooling? Temp diff across the coil and heat ex barrel?
    As far as the vfd on the motor it all depends on what kind of equipment you have if the tower has a gear drive you spin it too fast or slow are you will ruin the gear drive, how cold is cold?
    North America
    Its a belt driven fan the min speed for the motor is 25 hz and thats our min on the drive. I am runninig a 2oF superheat with approx 1.5 oFTD across the barrel. I set the lift septoint to 45 and my chiller going into alarm has quit.
    Jul 2009
    You should see +10 td deg across barrel and 15 deg superheat your not exchanging heat clean the barrel it's prob fouled whats the ref pressures suction must be low, with 2 deg superheat you should be worried about moving oil do you have an oil sight glass check oil level prob all in evap
    North America
    Its Oil free machine im running unloaded about 12%fla on a flooded evap.
    Nov 2008
    For infrequent trips you can hook up an event recorder for solving knotty troubleshooting problems.
    http://www.google.com/search?hl=en&s...&aq=f&oq=&aqi=
    Wichita Ks
    Quote Originally Posted by chrishvacman View Post
    A WMC is a McQuay chiller with a turbocor compressor, no oil. 2 degrees is fine for the chiller. The only time he might see 10 degree across the barrel is at full load and if that was design.
    Jul 2009
    Well Centrifugal Chillers can be a pain in the a$% as we all know low pressure is different sorry didn't see the wmc thats a mcquay so call em up tell them what you have and they will tell you exactly what to look for.
    Ohio
    You also might want to run your tower VFD down to 18-20hz min.
    Western Wa
    You can probably get away with 15Hz on a fan, which is a variable torque load.
    I service one that is two compressor but also kind of a low load system.
    The tower is VFD fan and the unit is set up on lift rather than entering temp.
    I can't remember exactly sitting here at home, but it seems to me it's set up at 40 or 45.
    You've gotta have enough DP across the compressor or it won't allow the thing to load up, due to the refrigerant cooled compressor, which as I'm sure you're aware, has it's own liquid line for cooling.
    I think you did the right thing, but there's a lot of people much more experienced with the Turbocor stuff around here. It will be interesting to hear their take.
    God Bless our Veterans
    God Bless the USA
    Bay Area California
    if you can, try increasing the min position on the exv...
    also set the suction alarm limit on the compressor up a little bit...
    Chiller Rob
    Ohio
    Quote Originally Posted by Randy S. View Post
    Yikes! Aren't you scared of burning up the motor at that frequency?
    Western Wa
    Depends on the application. Most everybody says 20 Hz as a minimum.
    You'd want to check for overheating, but I've seen it done. The ones I saw it applied on were considerably below FLA at 60Hz. So, you could say that they were already derated for under 20Hz.
    God Bless the USA