    Air leaving cooling equipment always 90% ???

    Is the air leaving cooling equipment always considered to be at 90% RH?

  2. #2
    Join Date
    Mar 2003
    Posts
    7,400
    Post Likes
    no,there can be many configurations to change that. one example would be hot gas reheat.

  3. #3
    Join Date
    Aug 2006
    Location
    Ohio
    Posts
    2,759
    Post Likes
    Or gas fired, or electric reheats.
    UA LU189

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    LOL...

    The air leaving the evap coil, is always a high RH%.

  5. #5
    Join Date
    May 2000
    Location
    In the classroom...
    Posts
    682
    Post Likes
    Quote Originally Posted by guitarboyled View Post
    Is the air leaving cooling equipment always considered to be at 90% RH?
    Yes, even after condensing moisture out of the air, the cold air has contracted (think ice cube on a t*tty) so the moisture that is left takes up a "relative" high amount of
    space in the cold air - the supply air has moved close to
    the Saturation Point Curve of the Psychrometric Chart.
    Prof. Koldenhott
    HVAC Instructor

    "Those that CAN...teach...
    PASSIONATELY!"

  6. #6
    Join Date
    Jul 2009
    Posts
    54
    Post Likes
    Thread Starter
    Obviously I was referring to the air leaving the cooling coils before any type of reheat.

    From a calculation point of view, do we consider that it's almost always at 90% RH.

    For instance is the Bypass factor always between 100% saturation and 90% RH?

  7. #7
    Join Date
    Apr 2013
    Posts
    3
    Post Likes
    From ACCA Manual P (First Edition) pg. 29 it says "In actual practice, a supply air condition which falls on the RSHR (Room Sensible Heat Ratio) line and has a relative humidity between 85% and 95% is a good choice". Also, "A supply condition that falls below the RSHR line can be used, but the room humidity will be lower than the desired design humidity and If a supply condition that falls above the RSHR line is used, the room humidity will be higher that the desired design humidity". I hope this helps.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •